TBH this does not sound very good, I'd at least get some BS951 clamps on those,,, et a good connectionWhat's the deal with this regards to testing etc As there is no ring circuit cpc's
The existing board appears to be connected to the conduit via a section of twisted cables (approx equivalent to 10mm2)
Sorry a slight misunderstanding, its boxed in so I can't see the ends of the conduit but they don't terminate into the fuseboard directly they are earthed by the twisted cable, I assume there ar appropriate clamps in place (possibly not though)TBH this does not sound very good, I'd at least get some BS951 clamps on those,,, et a good connectionOtherwise it's not a problem to use conduit as the CPC, just test your (R1+R2) as normal
Have you done any continuity tests to check the integrity of the existing conduit joints, such as opening up some of the accessories to check what the joints look like at the back-boxes and a long lead test?. If the conduit as CPC is dodgy have you got enough room to pull a new CPC through the conduit with the circuit conductors if you need to?Sorry a slight misunderstanding, its boxed in so I can't see the ends of the conduit but they don't terminate into the fuseboard directly they are earthed by the twisted cable, I assume there ar appropriate clamps in place (possibly not though)