That was my point, then it isn't a 10mm earth, it is a 10mm bonding conductor with the cpc being the earth. They both need connecting each end or they will not work as intended.Excellent point Batty! The cable runs will be boxed in where they run up the walls. So I will be fitting 63A RCCBs as isolators for each flat.
The concensus from various sources seems to be each flat should be treated as a separate installation as far as bonding is concerned, hence the requirement for the 10mm earth.
The water and gas services into the property will be bonded to the MET with the landlord's supply and each flat will be bonded individually via the 10mm.
If you are thinking of fitting RCDs to protect buried cables I assume you need 30mA. How are you going to provide descrimination against the rcds in the flats? Wouldn't it be better to use swa and forget the rcd at the origin. If it isn't TNCS then you can probably do without the 10mm then too.