Dave,
I am more than aware of the danger of the 5sec disconnection time on the inverters vs the 0.4 sec disconnection time in the regs.
There are still ways that this can be wired incorrectly by installers, it is not foolproof.
If you have non RCD ways in the CU you can connect into there, thus feeding into the load side of the RCD's and their associated final circuit MCB's.
There is insufficient clarity in the regs, the solar guidance etc. and a distinct lack of understanding with a LOT of Solar Installers of this issue.
This is ONE of the issues I have already highlighted to "higher powers" and been ignored over!
I am also not the only one to have brought this up.
Anyway back to the mixed MCB thing.
Wozz mentioned in post #37 a point which is moving towards the crux of the matter.
The issue is not with 60898, the issue is with 61439.
Machinery control panels will be built to neither, they will be built to 60204.
Also the manufacturer of the panel will be CE marking and certifying their panel in accordance with the statute law requirements.
Thus they will be undertaking the testing, verification, design checks etc. to provide a declaration of conformity or a certificate of incorporation stating compliance with the relevant requirements.
So one needs to look at this from the other angle, it is not 60898 that precludes their use it is 61439.
You are tampering with the design and certification of the assembled board.
As I have stated, I don't like it, I don't agree with it, but, they have a pretty water tight case as the law and standards sit at the moment.
If you put a "non-standard" MCB into a board, you take on the responsibility for the design, and certification of that assembly in compliance with the product standard.
Would you put a Phillips magnetron into a Bosch microwave if they were obviously different and modify the Bosch unit to accept the Phillips magnetron and then provide this modified microwave oven back to the customer as acceptable?
If you are going to undertake design, modification or build of electrical control panels, motor control centres, panel boards and distribution boards, then I bet that your insurer would be interested?
As if you are fitting a non standard MCB, this is effectively the "case" that the board & MCB maker would be putting together on behalf of HSE, you would also find yourself in non compliance with 7671, manufacturers instructions etc.
As I have said several times, I don't like it and I don't agree with it, however, we can't get away from it.
It is also illegal to sell product without the correct instructions etc. being provided, so B&Q are in breach of the law selling those MCB's in Spec's post #43.
It is quite a complex area of law, and it is rarely used, however, if you have been involved in product acceptances and CE marking of products you would understand.