Evening all, just want to run a query past you if I could. A 3 phase supply has been installed on a site and I have been asked to 'just run a cable in'. This proposed supply would initially be to an existing 63A CU that needs replacing and is currently run from a domestic CU on site. It is approximated that the run from new 3 phase to said CU is 100m and multicore SWA would be buried. Consulting 4E4A table I have values of 75 and 96A for 16mm and 25mm respectively giving Mv/A/M of 2.5 for 16mm. Using the formula for VD 2.5x63x100÷1000 I get a VD of 15.75 suggesting 25mm+ will be required. Could anybody advise on permissable % drops for SWA. Thanks in advance