i got this last year and can`t find the answer to 10mm two-core mineral insulated cable with copper conductors and sheath and an overall covering of pvc. i have got the 17th onsite guide could the answer been of the old regs 16th ed ?
question
a single phase circuit is wired 10mm two-core mineral insulated cable with copper conductors and sheath and an overall covering of pvc.if the design curent (ib) is 65A AND THE LENGH of the cicuit is 40m. calculate the voltage drop in the curcuit ?
4.2x65x40/1000 = 10.9v
where does 4.2 come from ?
question
a single phase circuit is wired 10mm two-core mineral insulated cable with copper conductors and sheath and an overall covering of pvc.if the design curent (ib) is 65A AND THE LENGH of the cicuit is 40m. calculate the voltage drop in the curcuit ?
4.2x65x40/1000 = 10.9v
where does 4.2 come from ?