maybe I never forwarded WIZ the paperwork or something?
If you want one i can PM you one?what about scrap dealers?in all seriousness tho, I really dont think I ever got one,
PM and email will be with you in 2 minutes.ok, if you can send it to my e.mail as well, is that poss,? then Agnes will write it down for me. that way I got no excuses. but now I'll have to think of some tips and tricks without killing WIZ along the way!!!
Oh bum!!Thanks SL...Borrowed neutral did come to mind, but I think not...
(Switching off other RCD, isolating remaining light circuits from RCD2, still causes a fault)
The 100 ohms is only in place when the LIGHT switch is on, (switch) LIVE to CPC..............not L to N..
AND I can have all other lights on up/down without any issues..
ALL other loads were removed during fault finding exercise..
Applaud Smiley
not wishin to rub salt in the wounds m8...does anyone else have one?
nIGHT EXT, let me know how bad the advice was, or what ward you are in so I know where to send the grapes!!!!!?
Im sure if you PM either myself or Admin one of us will get a password made up for you.Talking of passwords i dint have it either could someone enlighten me as i am a qualified sparks :^O well of sorts anyway :^O
http://niceic.org.uk/contractordetails?orgid=131270321547235 there is the proof
soz, rubber band snapped in my laptop!!!!I think you've upset him SL, hes gone offline ; \
let us know how you get on.Off to work I go.....
well at least you found the culprit anyhoo.BORROWED NEUTRAL...Give you more details later..
:_| :_|
Well, having never experineced one of these before, one doesn't really know where to start...BORROWED NEUTRAL...Give you more details later..
:_| :_|
As long as it's one of those Special Editions ones...Well done exto - and congratulations on finding your first "Borrowed Neutral".As a prize - would you like a FULL Twix? :|
Glad you found the culprit bud!Applaud SmileyWell, having never experineced one of these before, one doesn't really know where to start...Very frustrating that my first 17th CU, and I get one.. :_|
Anyway, having been given good advice here.. I preceeded to find the problem today..............
Sometimes you can't see the wood for the trees when things go wrong...
Anyway:
Landing ceiling rose (heart of the problem)
Took the bull by the horns and got Landlord to pull carpet and flooring up, immediately above (Loft conversion:^ O)
And there it was, inaccessable JB...
Supplying Neutral & CPC (plus loop lives to rose).......
(And I could see switch wire from downstairs lighting circuit aswell)
Sods law my first 17th, should get this....
Now the easy bit getting the Neutral up stairs...
*