Hi All,
It gets better than that!!! Here goes for another of my weird newbie theories!!!!!!! [Tin helmet on!!!]
Now then; Lets say you have a "multiple occupancy" steel framed building, say a portal framed jobbie with ten units in it.
Now then..... The DNO will only provide a TNCS supply to ONE unit, all the others will have to be TT'ed.
Now, why is this then????? Well, think about this....Say they were all on TNCS...
So, the neutral is connected to the MET in each unit by the earthing conductor, and the MET is bonded to the steel frame.
Now, what is going to happen when all is up and running?????
The current will arrive at any particular unit down the relevant phase conductor. BUT, it will NOT necessarily go "back down" the corresponding units neutral. What will happen, [remember now, neutral is connected to the MET which is bonded to the steelwork] is the neutral current will travel through the steelwork of the building until it finds the neutral conductor with the lowest impedance, and it will go down there instead.
You could end up with the power from ALL the units trying to return down the one neutral. Result, one cooked earthing conductor from the MET to the neutral block, and one cooked neutral in the service cable belonging to whichever unit has the lowest impedance neutral [the one with the shortest service cable i guess]
Now then, back to our street of houses.... The whole street will have their neutrals connected to their MET's which are in turn bonded to the metallic water pipe in the street.
As the various neutrals will have various impedances, and at various times will have different volt drops across them [depending on the load they are carrying], the current trying to make it back to the transformer will "pick and choose" which neutral it wants to return down.
Whatever happens, it is EXTREMELY likely, a positive certainty in fact, that someones elses current will, at some time or other, be coming along the water pipe, popping up into your protective bonding conductor, travelling along it to your MET, down your earthing conductor to the neutral block and back to the LV main..
Hence, it is entirely possible that YOUR bonding conductors will at various times be acting as a return for several properties, which is why the DNO make you have an increased conductor size on TNCS.... [cos they know all this!!!!]
Daft system or what.....
john...