Hi Sellers,
"Next door may have a lower impedance on their neutral but i highly doubt the impedance would be less by the time it goes through my bonding and water pipe through their bonding and down their neutral? Therefore it would go down my neutral"
Hmmm, not so sure; You are of course right up to a point, but houses just a few doors away from you might all be bonded to the same metallic services as your house, but fed electricity from a different feeder cable [with different impedance to yours] but all connected to the same supply transformer, and therefore, there is no knowing what happens as the load on the network changes, but be assured, problems with overloaded neutrals caused by different supplies bonded together, are a well known problem for the DNO's hence the TOTAL ban on a steel building having more than one TNCS supply.
john...
"Next door may have a lower impedance on their neutral but i highly doubt the impedance would be less by the time it goes through my bonding and water pipe through their bonding and down their neutral? Therefore it would go down my neutral"
Hmmm, not so sure; You are of course right up to a point, but houses just a few doors away from you might all be bonded to the same metallic services as your house, but fed electricity from a different feeder cable [with different impedance to yours] but all connected to the same supply transformer, and therefore, there is no knowing what happens as the load on the network changes, but be assured, problems with overloaded neutrals caused by different supplies bonded together, are a well known problem for the DNO's hence the TOTAL ban on a steel building having more than one TNCS supply.
john...