Wow, wow, wow
Aug 5, 2014
8,714
1,306
Woking
Well, I was chatting to a letting agent this afternoon and asked her how the mandatory EICR’s are going
her response “nearly all are failing”
this agent manages property in one of the most expensive and exclusive areas around here, so I’m guessing they are coming out as “unsatisfactory” because they don’t meet the 18th edition
what a farce ........
Yup and the HOC have well and truly courgetteed up haven't they ............. as I warned them😀
you always I&T to current standards. they havent exactly courgetteed up by stating this. its the so called 'electricians' doing the I&T that are not doing it correctly
"they" are saying the law says the rental properties must comply with the 18th edition
had another "report" yesterday.
Sparky emails lettings agency, lettings agency lists issues (no reg numbers) and a quote to put right
No unsatisfactory EICR has been provided ...................
This is interesting .      It always stated that , as Andy says,    you test PIRs & now EICRs  to the latest Regs .    I believe this time they actually stated  "  testing to the 18th edition " .
That would imply to many sparks that that if he can't see a metal board , a lightening strike over current jobbie  and  whatever that other thing  was that no one fits ..it must be an " Unsatisfactory"    result.       Totally forgetting that the place as deemed to be safe during the 16th   & 17th  editions  say.
I think the answer  to all this lies in the coding  chosen by the tester .
I have a question on testing  but don't want to cloud  this thread  so create a new one .
I'm guessing the board isn't metal...
I went to see this property yesterday - and only did a visual like the other "spark" had done and according to the tenant he just walked around for about 30 minutes
My conclusion is that the other spark arrived on horseback
I recommended the landlords undertake a proper EICR so the true situation can be assessed - and they have agreed with me - watch this space
Had one yesterday
NO RCD.....C1...........it's a 2013 board with RCD main switch
board is plastic. ......C2
sockets are single and unswitched ...C3
not enough sockets....C3
No earth on lighting...C1
loads of others these are just the ones I can remember.......all on a list, no official certs or anything
estate agents wouldn't tell me who had done it
Had one yesterday
In bold - that's an interesting coding !
Had one today
customer rings me and asks if I can have a look at a report that has been done on her rental   ( I couldn't do the EICR due to my current project)
firstly it states on the top line
Visual Condition Inspection!......and cost her £60
Mains
PVC C2
NOT compliant with IP4X C2
bathroom
light fitting  not suitable for area C2
complete inspection took less than 15 minutes
New metal board required. £500 ( present board is a split load twin RCD board )
in order to issue a Current Safety Certificate we recommend that those items which do not meet standards BS7671 are rectified