This time last year I undertook a periodic for a customer at one of his rental properties.
Came up with a few code 1's that have all been sorted (by his handyman :C ).
Also gave a 2 for green goo on the immersion & spured socket for shower pump in airing cupboard & another 2 for the spur being on the immersion circuit anyway.
At the time he asked what needed to be done with the circuit & green goo. I told him the circuit tests fine but keep an eye on future IR readings on future periodics as it is currently low but ok (R1+R2 = 0.17 IR >20Mohms Zs = 0.42 ) & the green goo is probably due to the ambient heating of 1960/70's cable from immersion tank & pipework, as no other circuits are suffering from the goo effect & the immesion circuit conductors at the cu end are clean.
I advised that the circuit terminations be cleaned & fcu + socket be changed (idealy the socket removed from immersion circuit & added to the ring main).
Now zoom forward to the present....new tennants move in & cant get pressure in the shower so call the letting agent with complaint, letting agent calls out a plumber (without notifying landlord) who rolls up & plugs in the pump.... hey presto the shower works.
Now the tennant sees the socket & notices green goo around the rocker switch (yes the my advice was ignored by landlord ) & promptly calls the letting agent to complain again the agent without notifying landlord sends in a local sparks, the message to the landlord from the agent..
" The electrician has looked at the socket & (reading from the report sheet)due to green goo I have turned off the circuit by removing the fuse. I advise the circuit be rewired asap as the green goo is a sign that the cable is old & breaking down"
The cost for the sparks to look at the green goo
Came up with a few code 1's that have all been sorted (by his handyman :C ).
Also gave a 2 for green goo on the immersion & spured socket for shower pump in airing cupboard & another 2 for the spur being on the immersion circuit anyway.
At the time he asked what needed to be done with the circuit & green goo. I told him the circuit tests fine but keep an eye on future IR readings on future periodics as it is currently low but ok (R1+R2 = 0.17 IR >20Mohms Zs = 0.42 ) & the green goo is probably due to the ambient heating of 1960/70's cable from immersion tank & pipework, as no other circuits are suffering from the goo effect & the immesion circuit conductors at the cu end are clean.
I advised that the circuit terminations be cleaned & fcu + socket be changed (idealy the socket removed from immersion circuit & added to the ring main).
Now zoom forward to the present....new tennants move in & cant get pressure in the shower so call the letting agent with complaint, letting agent calls out a plumber (without notifying landlord) who rolls up & plugs in the pump.... hey presto the shower works.
Now the tennant sees the socket & notices green goo around the rocker switch (yes the my advice was ignored by landlord ) & promptly calls the letting agent to complain again the agent without notifying landlord sends in a local sparks, the message to the landlord from the agent..
" The electrician has looked at the socket & (reading from the report sheet)due to green goo I have turned off the circuit by removing the fuse. I advise the circuit be rewired asap as the green goo is a sign that the cable is old & breaking down"
The cost for the sparks to look at the green goo