Hi BatsProbably your meter is not that accurate. What do you have? The most accurate ones seem to be the ones that send 25 amps down the cables. I have an old robin with d-lok usually if you test with this the readings are a bit lower than with my fluke 1652.Batty
I think what he's getting at is that the Megger might not be accurate in general, not that it is wandering over time.I've got a Fluke 1652, which I check monthly with my calcard and readings have been ok.
just thinking but if you rcd everything like a tt would you need a rod?Only steps you can take really is contact the DNO. If they can get it back to <.35 then great, if not stick a rod in.
Still doesn't change the fact that the Ze is .4 on a TN-C-S.just thinking but if you rcd everything like a tt would you need a rod?
calcard will not check your loop though.Hi BatsI've got a Fluke 1652, which I check monthly with my calcard and readings have been ok.
Will contact DNO tomorrow.
Cheers to all.