Hi cmacca81,Quote:ADS From reading the above, i thought it would be vital that Z's readings are below the maximum tabulated values to achieve disconnection time of an mcb within the given parameters.
I am one of the sparks who totally believes in the above statement, so for that you are right, in my mind.
I'm not one of the 'high Zs-bang a RCD on it' brigade
Are you sure you've read the other section properly, though.
Supplemetary bonding is, as it says, 'bonding'. It's used as 'additional protection' against electric shock - similar to using a 30mA RCD.
Supplementary bonding re-enforces your main protective bonding and helps to maintain the equipotential zone.
It works by re-establishing the equipotential reference at a particular location (e.g. a bathroom), between all extraneous and exposed conductive parts, to minimise the touch voltages between them under earth fault.
It, therefore, has nothing to do with 'earthing' - e.g. cpc, Zs etc.
'Exposed conductive parts' will sometimes be earthed to a cpc, but that is to earth the exposed conductive part, not to lower the resistance of the cpc.