  1. A

    Ring main.

    Sorry late reply. What was the question il try answer anything????
  2. A

    Ring main.

    Sorry late reply. What was the question il try answer anything????
  3. A

    Ring main.

    Thanks for the reply much appreciated I will buy gn3 and try get my head around the results. 
  4. A

    Ring main.

    I mean R1+R2? I'm trying but still quite can't understand how to find a N-E fault in the future quickly. Using that method 
  5. A

    Ring main.

    I have not mUch just got 3 years experience of installing but hardly any on fault finding so my understanding is limited. So how dangerous would the n-e fault be ifi had left it? As I had nipped the N on the back box when putting front back. I would like to hear the risk behind it plz? Since...
  6. A

    Ring main.

    Different ocpd? What kind? All very new to me. So far everything is on and working. Not been called back.Get EFLI Test on all sockets. Highest reading is 0.95 ohms. 
  7. A

    Ring main.

    I solved the earth problem but then doing so I somehow nipped the N. had two faults 
  8. A

    Ring main.

    What would the risk be if I had left one earth in? If everything was earthed? Could you plz explain the risk plz? Obviously it's sorted as I found the fault and corrected it but out of curiosity and just help understanding please. Thanks anyone? 
  9. A

    Ring main.

    No I don't have a copy. If not I will try get my 2391. I know the pass rate is low but for today I would like it!
  10. A

    Ring main.

    Well I blame my boss. I knew I would find it he just expects this kinda thing. I was never going to leave it unsafe and never leaving until it was resolved. So nothing was dangerous. However using the internet can't see nothing wrong with that. I never done that before. I told my boss get...
  11. A

    Ring main.

    I think actually my boss is doing that. I'm just trying to do what he says 
  12. A

    Ring main.

    FINALLY I SORTED IT! The N was nicked and touching earth. All done. I did all tests to confirm. Rcd continuity loop end to end and IR. NO MORE COWBOY. Lesson learnt. Thanks everyone. Was just that simple. 
  13. A

    Ring main.

    I know. I have all test equipment but this is crazing me Help
  14. A

    Ring main.

    Ok I'm testing the earthfault loop imp. Fine at every socket. Just when earths are together at one socket the rcd trips. Customer wants no mess no floor boards up. What can I do?
  15. A

    Ring main.

    I've Split the ring at one socket everything stays on fine but then join earths together rcd goes out. All sockets show earth connection when them earths are separate but goes off when joined together again. confused. 
  16. A

    Ring main.

    Nobody can get here. How should I leave this place then until someone can rectify it? What should I do as a temp fix? Anything possible? 
  17. A

    Ring main.

    Ok so how do I this? I will fix whatever it is. I'm all alone on this job. What do I do and what could it be? The Rcd stays in when earth at one socket is disconnected. Split the ring into two radials on 2 20a mcbs? Can't get to cables as customer doesn't want any mess at all. Won't pay for it...
  18. A

    Ring main.

    when earths are connected rcd trips on ring main. But when they are separated it stays on? Sorry for confusion I'm not a sparky I'm a sparks mate. Just trying to solve it. Never done much fault finding  I get loops imp readings everywhere though? Could I do away with the socket altogether? Just...
  19. A

    Ring main.

    my ring main earths are two radials is it unsafe? Or just not to regulations? My L go in a ring and also my N. 