Those aren't areas I'm concerned about.
This has to be a wind up ..........................
Those aren't areas I'm concerned about.
Already sorted, many thanks.
I'm gobsmacked that any company who claims to install chargers would allow somebody to go ahead and pull cables without a site visit and issue of some guidance ..................... madness.
Only just noticed this post, agree 100%! I could only see two realistic workable solutions for a supply of this type. (a) EV charger company does all of the work including supply back to DB and issues all certs etc upon completion of the job. or (b) EV charger company issues a specification for a supply to be made ready for their staff to connect onto, providing that a full EIC is available to confirm that the new supply is up to their specification before they energise their new charger.
Bottom line is that at the end of the day someone has to take legal responsibility if a property burns down or someone gets a fatal electric shock. Which when talking about these sort of loads can become a significant hazard if not designed correctly. On the news today I heard an article about Which promoting a campaign to reduce the number of dangerous electrical products in the home. https://campaigns.which.co.uk/product-safety/ There are an increased number of house fires caused by things like fridges, freezers, tumble Driers etc. and I will not be at all surprised if in 4 or 5 years we are not seeing a problem with complaints and failures due to dodgy cheapskate EV charging points causing fires and the like.
Doc H.
I believe that there are two ranges, one that runs on a 16A commando, and the other that runs on a 32A, then you have the 3ph units, which go up to 32A 3ph I believe, I'm no expert either, and I've not read the IET CoP, not sure I'll bother.I am ignorant of many many things ( see wife for further details) BUT
what sort of current do these chargers draw? And how long are they usually drawing this for?
just curious
Ooooh....I wouldn't want some weak of wrist ''5 dayer ' connecting one up for me!I believe that there are two ranges, one that runs on a 16A commando, and the other that runs on a 32A, then you have the 3ph units, which go up to 32A 3ph I believe, I'm no expert either, and I've not read the IET CoP, not sure I'll bother.
However, I gather they run at full current for hours on end.
I am ignorant of many many things ( see wife for further details) BUT
what sort of current do these chargers draw? And how long are they usually drawing this for?
just curious
I am ignorant of many many things ( see wife for further details) BUT
what sort of current do these chargers draw? And how long are they usually drawing this for?
just curious
One other thing to remember, is that based on 32A for 4 hours 365 times a year, a 10mm sq cable at 20Deg C will cost you 60-62 kWh of electricity in losses.
This will increase above this though, because of the heating effect of the cable caused by these losses.
If you use a 16mm sq cable the losses based on 32A for 4 hours 365 times a year would be 38-39 kWh, again at a cable temperature of 20 deg C.
I don't have enough data on the install to correctly model the cable temperature, but bear in mind that energy will increase in cost, the current flowing through the cable will increase its temperature above 20 deg C, as its temperature rises the Joule heating losses rise, whilst 10mm sq is rated above what you are looking at current wise, look at the difference in cost of 10 - 16 mm sq now, look at the difference of 21 units of electricity now, annually and into the future, and see how much the payback would be on the larger cable.
Plus you will have a lower volt drop and EFLI.
Using an online "wholesaler" the 16mm works out £8 more expensive than the 10mm for 40m.
21 units @ what 15p/unit?
£3.15 so payback in < 3years for fitting the larger cable.
That's a very quick calc, and not looking at cable heating, so the payback may well be < 2 years.
Your spark should be working this out for you when it comes to large constant loads, else you need to find another spark.
...
Anywho, it's all laid at 10mm2 now!
So your spark is not doing the whole job?
You are DIY'ing some of it.
Are you in England or Wales?
If you are in Wales, it is "technically" illegal and fraudulent for anyone to sign off the work of another under "Part P".