Right, I will try and simplify it, I recognise it is not particularly simple to envisage, although not that uncommon. Here we go:
100A (definitely) service fuse feeding, via 25mm tails, the "main" meter.
From this meter we go into a Henly block with 16mm tails. (There is also a small CSA single black (neutral obviously) cable which goes from the first meter to the E7 meter, but this is probably irrelevant I just didn't know what is is for)
The Henly block can only accept 16mm cable
From the block there is a feed to the "day tariff " CU, the E7 tariff Meter/switch, and 2 other small switch fuses feeding the shower/cooker, all in 16mm.
From the E7 meter/switch, there are 16mm tails into a 3036 fuseboard feeding the storage heaters. This is only powered up when the E7 meter/switch receives the signal to kick into life, obviously.
So, the whole cupboard housing all this is pretty rammed full of cables and units. So much so there is little room for the network supplier (WPD) to fit an isolator between the cutout and the meter.
The customer has contacted the electricity supplier, who have no interest, seemingly, in wanting to remove all the now redundant, E7 kit. It is obviously easier for both the meter reader and the customer to submit reading from 2 meters, one of which will never change. The clearly do not want to send a "subby" to site.
When I upgrade the CU I will be expected to fit 25mm tails. Unless I thought there was no chance of my scheme coming to look at this as part of my next assessment, I would not give a hoot, but I know they will bring up the 16mm tails. I know, as we all do, that the 16mm tails are perfectly adequate for the prospected current draw, but this is seemingly irrelevant.
So, I need to try and bring some sense into all this, I was just trying to see how other member might deal with it, bearing in mind the customer is a tad fastidious, as well as tight, as is usual.
Yes, I have a bag full of meter seals, and could easily pull the service fuse, but I would still not be able to upgrade the tails from the first meter to the henley block, so no point. Same if WPD fitted an isolator, which they can't really (no room). And my refitting the seals is of no real point.
I would install my new CU and dead test it, and then get the meter provider to connect the tails into the meter, but it would need to go via the henley block, which is the customers (my) responsibility, as bypassing it would mean the E7 meter is now dead, which is, apparently, not something they can do.
I might be making the mistake of trying to be too politically correct here, and should just get on with it. Believe me I have a few other means of sorting this out, as Murdoch is probably alluding to. I was just looking for a bit of advice.
I think the easiest solution would be to stop worrying about the 16mm tails from the meter to the henley block, go with 25mm from there to the new CU and not disturb any seals or involve anyone else, if you get my drift.