OK, To be controversial not like me!
I would NOT use a socket at any time any place (thats Martini! :innocent ) unless I HAD to.
Next I would never use SWA to any machine which had a motor unless the possible motor vibration was minimal. My shout based on my experience of rotating machine design, the application the condition of the machine and the likely maintenance routine primarily, unless specific manufacturers vibration levels were available for the machine elements in question.
I would NOT use flex in any industrial situation for more than about 1m without some additional mechanical protection.
I would use either SY, (braid earthed, glanded with GXD's) or metallic flexible conduit on the supply. Would not rely on the mechanical protection for cpc on either (it's not allowed).
I have done almost this job, but my recycling machines were pulling 125A per phase and the other was 200A!
I had to run SWA to the connection ponts, not happy though, due to the possible vibration affects on the cores and the possible work hardening to the strands with the subsequent enhanced risk of probable fatigue failure of the copper strands in the SWA. Seen it, and with 6491x.
Neither are suitable for connection to vibrating equipment, and any rotating machine vibrates, it's just the frequency and magnitude that varies, and these havebroadly differing affects on associated equipment.