If cables are concealed they are going to need 30mA Rcd protection unless they are protected by earthed metal or earthed swa so that will not comply with 17th. You also will need an 80 amp switchfuse if its a 100 amp supply so if there is a problem your fuse will go before supply fuse.I think KME has already clarified, but NO RCD required for TNS or TNCS.It may be required for TT to provide Shock protection as earth loop impedence will likely be more then max Zs for the Distribution cct.
Why Switch FUSE?
The DNO will only allow THEIR Service fuse to be used to protect YOUR Meter tails up to 3 Meters in length. More then that then YOU have to provide Fault and overload protection.