433.1 Every cct shall be designed so that a small overload of long duration is unlikely to occur.
Now 433.1.5 is a paragraph which is a progression from the above reg. So can a small overload of long duration be created by sticking your very tiny thin fingers in a socket?
433.1.1 the protective device shall not be less than the design current of the cct
This design current will be 13amp (to a s/f/s)
433.1.5 is just a reg specific to ring main ccts, with a bit in it that says "under intended conditions of use, the LOAD current in any part of the cct is unlikely to exceed FOR LONG PERIODS the current carrying capacity of the cable"
This reg being to do with ring ccts has nothing to do with the radial scenario, even though it supports it.
433.2.2 The protective device, protecting a conductor against overload MAY be installed ALONG THE ROUTE, provided it fulfils AT LEAST ONE of the following conditions.
This means that it doesnot have to comply with both.
(1) it is protected against FAULT CONDITIONS with requirements of section 434
(2) its length does not exceed 3M AND is installed in such a manner to as to reduce the risk of fault.
Section 434 protection against fault current
434.1 The PFC shall be determined at every point of the cct.
434.5.2 For a fault of VERY SHORT duration KsqdSsqd shall be greater than the value of let through energy for the protective device.
After checking through the BRB at the above regs, I am now convinced the radial scenario is acceptable, as long as the MCB protecting it, is within the range for protecting the cable under fault conditions.
come on......can anybody do the calcs to show that a 32A mcb will infact protect a single 2.5t&e cable under fault conditions