[quote name='Lee
For reference (and before people accuse me of slanting the question) as its not on the reply, here is my initial email:Thank you for your email.I am required to preface my remarks by saying that I have no authority to interpret the requirements of BS 7671:2008 Requirements for Electrical Installations as that is one of the roles of the Joint BSI/IET Committee JPEL/64/ however, within that constraint I hope you will find my comments helpful.
BS 7671:2008 is an installation standard for the fixed electrical installation not a product standard. Please see Regulation 113.1.
Regulation 433.1.1 makes it clear that the operating characteristics of a device protecting a conductor against overload shall satisfy the following conditions:
(i) The rated current or current setting of the protective device (In) is not less than the design current (Ib) of the circuit, and
(ii) the rated current or current setting of the protective device (In) does not exceed the lowest of the current-carrying capacities (Iz) of any of the conductors of the circuit, and
(iii) the current (I2) causing effective operation of the protective device does not exceed 1.45 times the lowest of the current carrying capacities (Iz)of any of the conductors of the circuit.
Hope this helps.
Hello.This was a question asked the other day and I wanted clarification on the correct answer as to whether its compliant or not.
A 32A MCB connects to 2 single runs of 2.5mm cable, one connected to a Switched Fused Connection Unit and the other to a Double Socket Outlet.
I believe this whole circuit does not comply with either 433.1.1 or 433.2.2 depending on where your overload protection is seen as being. It has been argued that the protection for the branch with the socket on is protected by the BS1361 fuse in the Plug but I believe that this is not suitable as the fuse is after the sockets and the plug could be easily removed therefore removing the protective device.
What is the official position on this circuit?
Thanks.
you never mentioned why you think the FCU doesnt comply in that email - only that the socket can have the plug removed (and incidently, if you remove the plug, there is no load connected to be able to overload the socket....). so, your whole argument for the socket not complying is the removeable fuse. does that mean you agree that the FCU complies, since the fuse cannot be removed from the circuit?I think we should close this thread as not even the IET want to touch it. Formatting is lost below but the (ii) section had been underlined:For reference (and before people accuse me of slanting the question) as its not on the reply, here is my initial email:
Ian this is the original question that started the whole thing. Your email does not reflect this. From reading your response from IET the circuit complies. The 13A fuse satisfies those conditions and is protecting the cable from overload.32A RCBO feeding two 2.5mm cables with a switched fused spur or single socket on the end. So one point per cable. I think yes, but i was told different today and i think they are wrong.
How do you read that when all they said was 'hope that helps'?Ian this is the original question that started the whole thing. Your email does not reflect this. From reading your response from IET the circuit complies. The 13A fuse satisfies those conditions and is protecting the cable from overload.
I've been away for a week can't believe this is still going will have to read when I have a lot of time.I've been away for a few days & i have to read 7 pages to get to the bottom of this shtiesummary please?
i wouldnt bother :^O :^OI've been away for a week can't believe this is still going will have to read when I have a lot of time.
Could you explain this from a design stage?The 'science' as you put it is pretty straight forward.Facts:
We require three forms of protection for any given circuit
1 Earth fault protection - provided by the RCD element of the RCBO
2 Short circuit protection - provided by the MCB or Cut-out fuse
3 Overload Protection - an overload can only occur if there is a load in the first place.
In the case of the radial with FCU, this is restricted by the 13A fuse in the FCU, so is impossible to overload.
In the case of the socket outlet, you are restricted to the two 13A plugs that you can plug in.
So, protected with a load, no need for overload protection without.
Pretty straight forward, I'd say.