a radial can have a branch at any point, including the MCB, so technically, its still only one circuitI would find it impossible to design two radial circuits sharing one mcb.
so that would be everyone who has added a spur to a ring main.Im going to state this again,anyone that designs a circuit with a cable capable of carrying 27Amps(at most) and protects it with a 32Amp device is at best unable to grasp the theory of :-
load current < design current < cable current
and at worst simply incompetent
but ive alreayd said before - sockets come under 433.3 - omission of overload, since the actual circuit doesnt contain the overload protection, the equipment plugged in does.Because, again, sockets are not suitable for overcurrent protection of preceding cable. 433.2.2 states that.
and eletrically the difference is? wheres your overload protection for your single 2.5 with a DSSO on the end?because quite simply it has been designed as a ring(compliant with regs) and a spur has been added(complying with regs)but can someone please explain to me how you can design a circuit to the following equasion and still comply
load current < design current > cable current
No, as I've said in earlier posts, I couldn't think of a single reason why I would design or install it this way.Could you explain this from a design stage?I would find it impossible to design two radial circuits sharing one mcb.
In all, regardless of what anyone thinks its just not good practice, I would have to read up on the science though.
Maybe Manator can enlighten us?
We are compliant due to reg 433.1.5and eletrically the difference is? wheres your overload protection for your single 2.5 with a DSSO on the end?
You have never shown this because you can not accept that a socket can not provide protection to the preceding cable. Even the IET agree to that hence have pointed out it doesnt comply with the regs too.No, as I've said in earlier posts, I couldn't think of a single reason why I would design or install it this way.BUT
Let's say, for arguments sake, that the said scenario came about because the two 2.5mm radials were once spurs off a 4mm radial.
For whatever reason, someone saw fit to remove the 4mm radial without changing the 32 A RCBO.
If I then turned up to do a PIR on the installation, I couldn't justify coding it a 1, and thereby failing the whole installation - it hardly presents an immediate danger.
And, as has been shown in previous posts, I wouldn't even code it a 4, doesn't comply with BS7671, because it does
I haven't read all the pages to this thread, and neither am I going to.In the compliance agreement posies' defence there steps, they claim that the fuse int he plug will protect that piece of structured cable.
So, once again, how do you explain the regs allowing a 2.5mm, un-fused spur, off a 32A ring final or radial??I am afraid threads like this boare me to death. The way I see it a cable that is rated at 28 amps in perfect conditions should not be used on a 32 amp circuit simple if you do its poor design of circuit and why would you want to do it anyway when you could use a 20 amp circuit breaker or two.
I find many threads on the forum boring, I would never comment on them to say so, I assume they are of interest to other members.I am afraid threads like this boare me to death. The way I see it a cable that is rated at 28 amps in perfect conditions should not be used on a 32 amp circuit simple if you do its poor design of circuit and why would you want to do it anyway when you could use a 20 amp circuit breaker or two.