Domestic PME, have two 2.5mm t&e on a B32 mcb, if this was a ring at sometime then the continuity is broken somewhere and i cannot locate the break. No access to underfloor, no spare ways in the CU, has RCD protection to 30mA. I'm thinking it is not compliant to put two Skt Radial cct's on one breaker even if i downrate to B20? Any advice on what to do here please. Thanks.
ALL three legs open circuit? L, N & E....?
On the balance of probability I would guess this NEVER was a ring...
Just someone (DIY bob or his brother) banging radials onto a 32A MCB cuz thats what they think sockets must be on irrespective of the cable size.!
What to do????
As the total number of sockets on this circuit is not Infinite it would not take too long to asses which sockets are fed off which leg of cable.....
1/ Do an Insulation Resistance test between the L-L & N-N of the alleged two half's of the ring...
just to verify there is absolutely NO continuity at all between them..
e.g. if it is a bad joint.. screw undone in the back of a socket.. you may get a high resistance reading.
2/ Take one cable OFF the MCB...
3/ Re energize the other cable..
go round with your ELI tester.. read AND note the Earth Loop Impedance at each socket...
4/ Write figures onto a floor plan sketch..
5/ As this is a radial the numbers should get bigger the further along the cable...
6/ Open up the socket with the biggest ELI
have a look if it has 1 or 2 cables into it!
7/ Do steps (2) thro (6) for the other cable.....
8/ If you have too "end" sockets that BOTH only have one cable in them..
then its more than reasonable to assume that it was never a ring in the first place....
9/ The longer way to do the above is to open up every socket and do dead resistance tests along the lengths of the various sections of cable.
Tell the customer you need to investigate the circuit as the previous electrician appears to have been negligent in either labeling of circuits, selection of protective device, testing prior to energizing a ring...
quote it at 10mins per socket + half hour thinking & mug of tea time..
If they say no....
walk away and leave it as it is!
:coffee
---------- Post Auto-Merged at 10:28 ---------- Previous post was made at 10:26 ----------
I think my post was just the slightly longer version of what Theory say in shorthand on post #11 :Salute
:^O