David_2013,
It seems you are miximg up earthing and bonding.
This is common among lay people.
The supply to the server rack must be "earthed", to the same "location" from which the supply is derived.
You cannot derive a circuit earth from anywhere other than from where the circuit supply originates, for it to be compliant, and more importantly, safe.
Also, if, your server rack when in use has earth leakage >10mA, then there will be an enhanced requirement for the circuit cpc's.
This is not quite as straight forward as it may first seem, not only for it to be safe, but also for it to be reliable.
If, your "earths" are not "suitable" then this can have a functional and reliability issue on your server rack, that could, result in premature failure and data loss.
You should also consider surge protection, as required by BS7671, and, I suspect the equipment manufacturers, which, I also suspect will have certain earthing, and, possibly bonding requirements,