Economy 7 boiler - no hot water

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

g2ps

Member
Joined
Sep 21, 2017
Messages
8
Reaction score
0
Hello.

Thanks for taking time to read this...

The flat in question is served by Economy 7. Currently, the storage heaters are working fine, the hot water works when on boost - but there's no hot water generated when relying solely on E7.

The tank has been fitted with new immersions and thermostats (by qualified plumber). As a test, we also switched the wiring from the boost immersion to the E7 immersion and that worked both ways, so we know the immersions are both working fine.

The wall switch in the boiler cupboard lights up when the E7 kicks in at night, so that seems okay.

The fuseboard has been checked (by qualified electrician), no trips or faulty wiring. The wiring to both the E7 immersion and the boost immersion have also been checked.

We have pressed reset on both thermostats.

If it's an electrical issue, if the E7 feed from to the flat splits (between hot water and storage heaters) when it gets to the fuseboard, then the problem can be isolated as occuring somewhere between the fuseboard and the E7 immersion connection.

If it's a plumbing issue, any ideas, anyone? We're completely out of them having, we feel, exhausted everything.

 
Thank you so much for your input, Sharpend. Very much appreciate your time. Electrician is going back tomorrow so will keep you posted!

 
Late to this discussion.

So you have checked the heaters themselves so they re okay. R1, R2 and Rn on the circuit is okay so no wiring fault

The bit that baffles me is "the light on the switch comes on when the E7 is on, so the time switch is also okay.

So one of those tests must be wrong, otherwise it would work?

The only other thing is send the spark round very late ant night or very early in the morning when the E7 is on to trace it through properly.

 
Late to this discussion.

So you have checked the heaters themselves so they re okay. R1, R2 and Rn on the circuit is okay so no wiring fault

The bit that baffles me is "the light on the switch comes on when the E7 is on, so the time switch is also okay.

So one of those tests must be wrong, otherwise it would work?

The only other thing is send the spark round very late ant night or very early in the morning when the E7 is on to trace it through properly.
or if the electrician can't or won't do that, the get him to connect a lamp of some description across the heater terminals, then ask the tenant if the lamp lit at all during the night.

 
Cheers, guys.

I have the sparky lined up tomorrow to do exactly that - to wire up a bulb/lamp to the E7 spur (despite this spur actually lighting up during E7 active periods. as proven by the tenant's photo of same).

Will let you know what happens...

 
Latest update... the electrician connected a lamp to the E7 spur on Saturday and, according to the tenant, it's been lighting up during the E7 timeframes.

So what now? Other than there being a fault with the cable from the E7 spur to the E7 immersion, I can't think what else it could be. What are the chances that this could be the problem?

 
Latest update... the electrician connected a lamp to the E7 spur on Saturday and, according to the tenant, it's been lighting up during the E7 timeframes.

So what now? Other than there being a fault with the cable from the E7 spur to the E7 immersion, I can't think what else it could be. What are the chances that this could be the problem?
Get a better electrician.

If the power is getting to the spur, yet not heating the water, and he can't find the fault, his fault finding skills are lacking.

 