Have been asked to supply a feed for a boiler. Now I'm aware of the Spur off a Spur, but wonder how this works??
Currently the customer has a switched FCU off the Kitchen Ring Final above the work top supplying a single socket for the washing machine. The wall is tiled and so to avoid damage to these, am wondering if I can take a spur off the socket underneath into an FCU down rated to 3A for the boiler?...One drawback is you cannot turn any power off to the Washing Machine without disconnecting power to the boiler as well...
As the Boiler is on a fuse and the Single Socket is fused off the plug top, would this be OK? Easiest and least amount of disruption...I'd only be using 4inches of cable to spur, protected by 3A at FCU and 13A off Plug top.
Currently the customer has a switched FCU off the Kitchen Ring Final above the work top supplying a single socket for the washing machine. The wall is tiled and so to avoid damage to these, am wondering if I can take a spur off the socket underneath into an FCU down rated to 3A for the boiler?...One drawback is you cannot turn any power off to the Washing Machine without disconnecting power to the boiler as well...