fire sealing in riser cupboards

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

binky

retired and loving it!
Supporting Member
Joined
May 7, 2008
Messages
15,121
Reaction score
2,042
Location
Sunny Plymouth
An independent inspection has raised the issue of a lack of fire sealing between floors in the riser cupboards. Building is 3 floors high and there is no control or switch gear in the cupboards. So 2 questions:-

1/ what are the legal requirements for fire sealing in risers

2/ a suitable solution. I was thinking intumescent material packed around holes or even the expanding foam stuff. Not being something I normally get involved with I'm open to advice.

2016-06-29 08.00.22.jpg

2016-06-29 08.01.48.jpg

 
Is that water coming through with electric? BC don't usually accept this, they like to see separation by means of separate compartments for water and electric. 

Usually a fire expanding foam is sufficient, although plumbs on soil pipes etc are usually directed towards purpose built fire collars. 

 
I personally would not use expanding foam. That stuff is lettuced. 

I would fit a trunking system on the one that has no trunking and then fit either fire pillows or intumescent fire blocks. These can then be removed and re-instated to allow wiring if required. 

image.jpeg

image.jpeg

 
Wouldn't expanding foam, or fire pillows for that matter, be considered to be insulating material? Therefore cable derating might need considering. Also derating for bunched cables?

 
I personally would not use expanding foam. That stuff is lettuced. 

I would fit a trunking system on the one that has no trunking and then fit either fire pillows or intumescent fire blocks. These can then be removed and re-instated to allow wiring if required. 

View attachment 7128

View attachment 7129


The reason I suggested Kerlane is it can be removed and reused. We used it for lining annealing furnaces running at 850°C continuously.

The astro-flame may look nice but how much are they?

 
i guess it depends if it goes to a different fire compartment?


I've done some reading, basically the riser is considered a fire compartment (if constructed correctly), so cables going sideways penetrate the fire compartment. Therefore there is some doubt if holes in ceilings are penetrating the compartment as the riser is the compartment, and I've seen modern blocks of flats 20 storeys high with no ceilings, just platforms at each floor. The one issue with that argument in this case, is that there is a good chance some cables penetrating the ceiling then go sideways before reaching the next levels cupboard. Just can't see if they do or don't. If they do, then I think intumescent sealing is required. There is another debate then if each cupboard should have smoke detector head in it as a sealed compartment?

 
Last edited by a moderator:
The reason I suggested Kerlane is it can be removed and reused. We used it for lining annealing furnaces running at 850°C continuously.

The astro-flame may look nice but how much are they?


Not huge costs.  Less than £50.

 