yep, got your PM george,

your not a million miles, Im just snowed right now,
Fair enough.  If you do get a chance, give us a call.  I thought you said snowed in - we were until recently!  Any chance of a visit very much appreciated! 

 
I have been watching this thread with interest , not because of the workmanship but because  of the comments.

Ok, the temporary works are very poor, but although i would not have done the job in the same way its not rough or piss poor or deserving of similar comments. I think the guy has managed to get a very tidy 1st fix on what seems a difficult hard surface. The only real problem is he's outside the safe zones. Maybe  its poor planning, he started in the zones but by the time additional cables were installed its taken him  out of them, who knows

Once again i would have not done it like this, i probably would have  used a diamond blade in a grinder to get a deeper channel in the zones with a bit of capping.

The OP did not answer if this is all just being skimmed or is there going to be board and or insulation over the walls, it makes a big difference .

Only last month we fitted out a kitchen/diner conversion in a house that had been rewired 8 months earlier (by a NAPIT guy) Very nice job, cert & part P done, except the main cable run up was  a 200mm wide chase in the middle of the kitchen wall . The room had not been decorated & when i cut away the plaster to have a look he had even put the data, phones & coax under a separate capping, so why in the middle of what was then the lounge wall.

 
I have been watching this thread with interest , not because of the workmanship but because  of the comments.

Ok, the temporary works are very poor, but although i would not have done the job in the same way its not rough or piss poor or deserving of similar comments. I think the guy has managed to get a very tidy 1st fix on what seems a difficult hard surface. The only real problem is he's outside the safe zones. Maybe  its poor planning, he started in the zones but by the time additional cables were installed its taken him  out of them, who knows

Once again i would have not done it like this, i probably would have  used a diamond blade in a grinder to get a deeper channel in the zones with a bit of capping.

The OP did not answer if this is all just being skimmed or is there going to be board and or insulation over the walls, it makes a big difference .

Only last month we fitted out a kitchen/diner conversion in a house that had been rewired 8 months earlier (by a NAPIT guy) Very nice job, cert & part P done, except the main cable run up was  a 200mm wide chase in the middle of the kitchen wall . The room had not been decorated & when i cut away the plaster to have a look he had even put the data, phones & coax under a separate capping, so why in the middle of what was then the lounge wall.
This is VERY helpful and goes with comments from the builder.  Three reasons got me motivated to post this thread.  One, I noticed this wiring job is a LOT LOT different to the methodical and neat way another electrician had re-wired my 1869 stone terrace - so you can imagine the brick work on that!  He put EVERY wire in conduit and realised that all the walls need plastering and did it all so that there were no problems for the plasterer.  This was my only experience of a re-wire so I expected the same standard and attitude this time round particularly as I had had a recommendation.  The other reason was the attitude of the guy who has been re-wiring the property.  It stinks and no housewife is going to trust someone who is acting like a right nutter rewiring the house her kids are going to live in.  My friend commented on how he was acting. At one point he laughed like a maniac hyena and I went away thinking - should I really trust this guy? He put a socket on at a sort of 65 degree angle. He corrected it when asked to do so but that's just one hint of how he was going about the job.  There are some plugs and sockets where everything is in safe zones and they run fine - so it begs the question - why are they okay and then the others are just plain doo lally in comparison? When paying good money for a re-wire, with a guy with a bad attitude, I think the punter is correct in checking it out. There's been other Jekyll and Hyde mentality in the house by someone else recommended by the same outfit so I want to play safe particularly with the electrics.  PLASTERING - they never asked us about that.  Builder says it's not a problem regarding insulation board on the exterior walls, skimming etc. They are willing to take skirts off etc to do whatever plastering is necessary. Plasterer took a look in the kitchen and said that even though things look uneven to us as punters, once the plasterer goes round it, it's fine. We are going to be in this house for the next 20 or so years and as I have taken photos of every room I will keep them as a record for the future. All ceilings to be boarded. All walls to be rendered/skimmed where necessary.  External walls to have insulation board.  Any further thoughts much appreciated.  :B-

 
The temporary supply via the broken fuse box is possibly the most concerning item. Live parts should always be covered, insulated or protected from contact by barriers or being placed out of reach. And temporary supplies are generally more hazardous than final fixed supplies, so even greater care should be taken.

Doc H.

 
Last edited by a moderator:
. PLASTERING - they never asked us about that.  .  External walls to have insulation board.  Any further thoughts much appreciated.  :B-

Ahh, Thats why i mentioned it. A ( what i think is not well thought out) regulation is if cables are buried more than 50mm then certain other regs are relaxed. From looking at the pic, your description & local council rules any outside wall (if  use of the room has changed) has to have insulation. In your case the easiest is on the inside as you can get plasterboard with the insulation prefixed to it. This is then glued onto the wall.  All you need is a total of 50mm including any board and finish and your cables are ok. I must add i still keep to the zones anyhow.

The electrician may have known this,  i always ask as it can  save time with chases and cable routes .

 
Ahh, Thats why i mentioned it. A ( what i think is not well thought out) regulation is if cables are buried more than 50mm then certain other regs are relaxed. From looking at the pic, your description & local council rules any outside wall (if  use of the room has changed) has to have insulation. In your case the easiest is on the inside as you can get plasterboard with the insulation prefixed to it. This is then glued onto the wall.  All you need is a total of 50mm including any board and finish and your cables are ok. I must add i still keep to the zones anyhow.

The electrician may have known this,  i always ask as it can  save time with chases and cable routes .
Once again, thank you.  Your replies are helping us put things into perspective particularly in light of the fact that the electrician has either ignored the subject of plastering on such a big renovation job.  You mention local council rules. My husband thinks that because this electrician is under NICEIC and is therefore self certified then we do not have to notify the council about a re-wire on this house.  The builder that came the other day mentioned using just 35mm insulation board. 

:pray

The temporary supply via the broken fuse box is possibly the most concerning item. Live parts should always be covered, insulated or protected from contact by barriers or being placed out of reach. And temporary supplies are generally more hazardous than final fixed supplies, so even greater care should be taken.

Doc H.
That's what I thought and because he's walked off leaving the house half done just because the loft is ready for second fix, it really irks me. The loft conversion company just want their part of it finished and don't seem to care that the rest of the house is a shambles of a hospital job. 

 
Hi looking at the photos, Im guessing it's quite a large 3 bed house with new loft con?

Looking at the photo Of the chase to the consumer unit I can count around 7/8 new cables to consumer unit, Do you know how many ring mains circuits (socket circuits) lighting circuits and is there a standalone smoke alarm circuit? How many circuits have been installed?

Also I can't spot any Main bonding conductors to gas/oil and water stop taps should be 10mm green yellow cable.

If your planning on living their for a lot of years I would recommend to try to future proof it as much as possible, ie get a cooker circuit installed in the kitchen, or a shower cable near to bath room, ie cables run from consumer unit into said rooms not energized tho. Just in case any plans change, better to spend a little extra now.

 
You just never know what's under the surface! Here's my kitchen:

Sam_1593.jpg


SAM_4609.jpg


I do like a bit of trunking though. Though I do it and it's an accepted safe zone I try and tube on horizontal runs between sockets.......then I think well I might as well do the verticals You're always going to get "nasties" on an old place. I NEVER knew I had hollow block walls till I started chasing out. Plasterboard fixings and a mortar gun sorted that!

SAM_1510.jpg


Some properly earthed localised steel conduit might help with your zone issues? That photo with the tape measure, light switch? Maybe stick in a double width box and use a grid switch?

 
Hi looking at the photos, Im guessing it's quite a large 3 bed house with new loft con?

Looking at the photo Of the chase to the consumer unit I can count around 7/8 new cables to consumer unit, Do you know how many ring mains circuits (socket circuits) lighting circuits and is there a standalone smoke alarm circuit? How many circuits have been installed?

Also I can't spot any Main bonding conductors to gas/oil and water stop taps should be 10mm green yellow cable.

If your planning on living their for a lot of years I would recommend to try to future proof it as much as possible, ie get a cooker circuit installed in the kitchen, or a shower cable near to bath room, ie cables run from consumer unit into said rooms not energized tho. Just in case any plans change, better to spend a little extra now.
Hi, it's a five bedroom house now as we just had a loft conversion.  The wires from the loft run straight down the wall on the second floor, through the ceiling of the first floor through one double socket in the hallway and then through the hallway wall to the CU in the garage.   We have 46 double sockets in the house, 3 single sockets, 20 x 1 gang switches, 2 x 2 gang switches, 1 x 3 gang switch, 3 fan isolators (one for a wetroom and two for bathrooms in loft and on first floor). This doesn't include the garage and wash house which are integral to the property. There are 3 telephone points, 2 tv aerial points for wall hung televisions. Each room has to have a smoke alarm in it because of the loft conversion.  The water stop taps goes over my little housewife's head - does this happen during second fix? He seems to have left quite a lot of work to do. I have no idea how many circuits have been installed.  :coat

You just never know what's under the surface! Here's my kitchen:

Sam_1593.jpg


SAM_4609.jpg


I do like a bit of trunking though. Though I do it and it's an accepted safe zone I try and tube on horizontal runs between sockets.......then I think well I might as well do the verticals You're always going to get "nasties" on an old place. I NEVER knew I had hollow block walls till I started chasing out. Plasterboard fixings and a mortar gun sorted that!

SAM_1510.jpg


Some properly earthed localised steel conduit might help with your zone issues? That photo with the tape measure, light switch? Maybe stick in a double width box and use a grid switch?
Why the hell couldn't the geezer in my house have channelled out neatly? Boo hoo hoo, a boo hoo hoo hoo hoo.  :_|   

 
You just never know what's under the surface! Here's my kitchen:

Sam_1593.jpg


SAM_4609.jpg


I do like a bit of trunking though. Though I do it and it's an accepted safe zone I try and tube on horizontal runs between sockets.......then I think well I might as well do the verticals You're always going to get "nasties" on an old place. I NEVER knew I had hollow block walls till I started chasing out. Plasterboard fixings and a mortar gun sorted that!

SAM_1510.jpg


Some properly earthed localised steel conduit might help with your zone issues? That photo with the tape measure, light switch? Maybe stick in a double width box and use a grid switch?
Now thats just showing off   Guinness

I would like to see the sparky get all those twin & earths down a 20mmm conduit  :slap

 
Not enough money in sparking for galv conduit. When the new regs came in I put a couple of cooker circuits through conduit so I didn't have to RCD protect them. It takes to long to install, these days they just get put through an RCBO.

 
This  place I did a few years ago had to be boarded as it was an external wall, the BC insisted it was 4" stud in filled with kingspan.

I cant find a picture of the wall at first fix stage, but this gives some Idea of the boarding that was required.................

http://i83.photobucket.com/albums/j293/gazjothomas/abbotts%20anne/1stfix.jpg

http://i83.photobucket.com/albums/j293/gazjothomas/abbotts%20anne/after1stfix.jpg
This is incredibly helpful, thank you.  At least at this stage we can check all this out between builder/plasterer and electrician.  :pray

Hey, this is the response from the technical dept at NICEIC.  I actually never meant to go through a boring complaints procedure - just to seek reassurance that this re-wiring job was going okay so I rang up to let them know that and they got back to me within 5 hours - result!  

[SIZE=12pt]Because the installation is only at the first fix stage, we are unable to determine the eventual condition of the works.[/SIZE]

[SIZE=12pt]We suggest that you discuss the matter with the contractor before he continues with the work, making him aware of your concerns and allow him to provide his response. You may want to bring to his attention the following electrical regulations: 522.6.101 and 522.6.102 which relate to wires running behind walls. If the contractor requires clarification on these, he is welcome to call our technical helpline who may be able to offer assistance.[/SIZE]

If after the work has been completed you wish to continue with your complaint, please provide evidence as to the scope of works ordered such as a contract, estimate or invoice and copies of correspondence between both parties, dated 1/12/12 and 28/3/13 as per your complaints form. Please also clarify whether the property is empty or in use.

 
Now thats just showing off   Guinness

I would like to see the sparky get all those twin & earths down a 20mmm conduit  :slap
I'll admit that a number of singles DID get used! It's all RCD protected anyway AND on TT to boot. The "plan" as the place is re-modeled is conduit all the way bay to a new CU filled with DP RCBOs.

 
I'll admit that a number of singles DID get used! It's all RCD protected anyway AND on TT to boot. The "plan" as the place is re-modeled is conduit all the way bay to a new CU filled with DP RCBOs.
Would you like to meet my electrician?  :slap

 
Would you like to meet my electrician?  :slap
Only if she looks like Kaley Cuoco, then I'd be prepared to travel / pay for my own and her flights, work for nothing AND do the whole job in STAINLESS STEEL CONDUIT  ;)  . The work though might have to take a back seat for <5 minutes a day though.

Actually I once worked with an electrician who would randomly break into Spike Milligan quotes and Goon Show esque laughter when in the middle of diagnosing a fault. Another fella was without doubt BRILLIANT. Slight problem, he was taking so many drugs you never knew whether he'd fix the fault in 30 seconds or "power down" mid diagnosis. Quite literally he'd dive in at 100mph then out of nowhere say "F**k this!", drop his meter and go off and hide for a sleep. Lost him once quite literally. Left site at Gatwick in two vans just before one Easter weekend as I had to go to the wholesaler I left most of my tools with him in his van. He was going on an Easter "cruise" around the Isle Of Wight. Basically a 4 day rave on a boat. I turned up on site on the Tuesday and "G" didn't. Our governor is going ballistic and I've all the materials but not many tools. He "surfaced" on the Thursday. They had basically clubbed together for the Captain of the boat to dock, take on more "supplies" and carry on going. His antics were legendary. And then at 26 he died of pancreatic cancer! 

 