I would concur with everything you say there Stringy!they are just normal 12v downlights each with there own 60va tranny looped in and out of a porkpie jb.....so there is hardly any distance between tranny and fitting just recommended distance.everybody i know does it this way and has done for years...ive never heard of anybody putting a clicks unit in a domestic property.
the only thing i can think of in his deffence is if you loop in out to the jb's you would get volt drop, the bathroom is only small though....but with the clicks unit they all come out from one place.
what do you reckon?
hes still a nob though hahaha
Re: voltdrop... you can always calc it?
say 1.0mm, 35watt bulb, 2.5m cable..
mv/a/m = 44
so....
44x0.15Ax2.5m / 1000 = 0.016Volts.
so 230v-0.016v = 229.98V @ your transformer!!! :^O :^O:^O
there again you may have slight difference of resistance on the individual bulb connections...
or the tolerance of the bulb itself!!! :O:OBlushing