Kitchen work

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

mikel

Well-known member
Joined
Jul 11, 2008
Messages
388
Reaction score
0
Location
Bolton
I've been asked to do some work in a kitchen that's being altered. It is going to have a central island of units with a work top. They want a power supply to it for some sockets and plinth lighting. The problem comes because the floor is 'solid' not sure yet what its made from but I'm unsure of the best way to get the cabling to the centre island. Anyone got any ideas on the best methods?

 
i once ran some cables along a floor chase when no other way. I ran them through some flexi conduit for a bit of protection, then a builder cemented them in.

I would maybe chase out the floor with a stone cutter, quite deep, then maybe try and put a small drain pipe to pull cables through or some flexi conduit

 
Get builder in to chase floor and lay some flexi in (a few runs) for future expansion too.

 
All the ones I have done in concrete floors I have used my chase cutter twice so to speak that way you have a 60mm cut that can then be broke out with a drill on impact function. These have been total refurbs so no need to worry about pipe under floors just be careful there are none if its not a refurb. I then run the cables through a 20 or 25mm conduit to the island once under the island they can just be loose.

 
Some older properties with solid floors are not that thick or solid at all, I would think an exploratory hole would give you a clearer idea of the best method. Chop out a small section of floor underneath where the island is going. A battery drill on hammer action will normally cut a depth testing hole and you can get the feel of how dense the concrete is. Lump hammer and hand chisel would probably be the careful way to go on this first exploratory hole, watching out for any other pipes or buried items.

Doc H.

 
My main concerns were what precautions you guys take to protect the cables, I was thinking of using some flxi conduit or the likes but wondered if steel would be better. Are there any regs to bear in mind. I can't seem to find any in the brb

 
You need to make sure you are not compromising a damp course too and other requirements that we do not normally have to comply with on a day to day basis, hence its easier to get a builder in.

 
Maybe you both should go read 522.6.6 again then. The clue is in the 6th word.

 
What about 522.6.5?

---------- Post Auto-Merged at 22:52 ---------- Previous post was made at 22:51 ----------

sproc you beat me to it!

 