Are there people here really questioning the values of 'adiabatic equation' ???? The values obtained by these calculations are far nearer to the actual cable size requirements than the simple play it safe then add a little more cable sizes found in the various tables in the Reg's. ...Far too many people treat the Reg's as some form of bible, when in fact it's a guide, ...but even the guide points you in the direction of 'adiabatic equation' in many areas..... The Reg's change from edition to edition while the adiabatic remains a constant!!!
The 'adiabatic equation' may well be an accurate form of calculation BUT, like anything, it depends on two very important things:
1) The person applying the equation and their ability to understand what they are doing and why.
and most importantly.....
2) The accuracy of the values input into the formula in order to perform the calculation.
Take the example mentioned by the OP, found in the NICEIC 'Snags and Solutions' book:
Here they use the following info to perform the calculation:
To calculate
I
Uo /
Ze = 230 / 0.18
Uo is an estimated amount (nominal) - the voltage is probably higher.
Ze is a measured amount - How accurate.....only the tester knows.
So we get
I at 1278 A
This is the calculated PEFC.
This is then squared and multiplied by
t
t is taken as 0.4 s.......hardly accurate, disconnection only has to be within that time.
Then the 'square root' is found of this number and divided by
k - from the regs.........probably the only accurate part of the whole formula (and it's a correction factor)
Some of these inaccuracies will increase 'conductor' size and some will decrease it, but, like I said, hardly an accurate calculation
And finally:
"It has to be acknowledged that the use of the 'Adiabatic Equation' to determine the CSA of an Earthing Conductor is by far more problematic than to select the CSA by referring to the Tables in BS 7671"-
Guidance Note 8, Page 23
---------- Post Auto-Merged at 01:01 ---------- Previous post was made at 00:55 ----------
''So, instead of his 0.18 Ze, he reads 0.12 - then 16mm required.....come on!! Are we really that accurate???''Well, if you were a mager contractors Design Engineer and used this philosophy, you would soon find yourself out the door. The difference between 100s and possibly 1000s of metres of 10mm or 16mm cable, works out to substantial cost savings.
If you were designing you would be dealing with lengths, CSA and resistivity - not measurement..........so the calculation would probably be more accurate - within your installation design.
But were talking about a one or two meter length of Earthing Conductor here, that people think you should be applying the 'adiabatic equation' to.