Where is the earth?Can anyone see anything wrong with this ??? TN-C-S ( PME )
havent you lot heard of that new style cable, called invisible :^O :^O:coatWhere is the earth?The Godfather
Like that on lol...........I have inspected this insallation and there never has been an Earth cable as the normal entry point is still intact...........I thought it was just me going Mad but no..... only Earthing there is is some bonding and a 4mm to the Gas and the Water .........tried doing a ZS test and the readings were very high ( 4.56 ) :zhavent you lot heard of that new style cable, called invisible :^O :^O:coat
if it says PME, then its suitable for PME if you want to use it. just because its there doesnt mean you have to use itNo I didn't fit a main earth was thinking about doing it but had to make sure that I would be doing the right thing...............
Will have to use it or i'm never going to get the ZS readings down What are the alternatives ?if it says PME, then its suitable for PME if you want to use it. just because its there doesnt mean you have to use it
First of all I would want to find where the 4ohms is from..Will have to use it or i'm never going to get the ZS readings down What are the alternatives ?
I would suspect this is a two wire loop test and the return via the neutral.First of all I would want to find where the 4ohms is from..e.g. is it though bonding?
or is there a Rod somewhere that you haven't found?
What other earth wires are in the CU?
For a TT system yes, but this is not a TT system as there is no earth rod anywhere :_| There is a earth wire taht comes out of the wall at the front of the house in to a little box thats fixed in to the ground ( see pics ) there is 3 earth wires in the cu, 1 from the gas, 1 from the water and 1 from bonding in the downstairs shower :coater... Ze can be upto 200 ohms, and Zs can be upto 1667 ohms with 30mA RCD....
That is the earth rod, so this is a TT systemFor a TT system yes, but this is not a TT system as there is no earth rod anywhere :_| There is a earth wire that comes out of the wall at the front of the house in to a little box thats fixed in to the ground ( see pics ) there is 3 earth wires in the cu, 1 from the gas, 1 from the water and 1 from bonding in the downstairs shower :coat
Earth spikeWill have to use it or i'm never going to get the ZS readings down What are the alternatives ?