The joys of living in the Highlands. I am trying to find a solution to a job 80 miles away, without making a 160 mile round trip to look at the job. I have lots of photos and emails from the customer.
It started out as "fix the burned out neutral bar" in one CU, and move the other CU to a new location.
I could replace the burned out neutral bar ( I have a spare) but told them I can't move the old CU, it needs a new one (no areseedee etc)
The logical thing would therefore be one new larger CU to replace the two existing ones.
BUT
Here's the loads:
12KW electric boiler presently on a C50
Immersion B16
smokes B6
Cooker B50
Shoiwer B40
Sockets B32
Sockets B16
Water Heater B40 *
Unknown B40 *
Lights B15 *
Unknown B32 *
It's the little Proteus CU with the C50 that has the burned out neutral bar.
But on the main CU it's the last 4 that worry me. B40A water heater? WTGrape is that? Lights on a B15? and what's the unknown circuits on a B40 and a B32
Clearly this can't all be settled without a visit to determine the unknowns.
Anyway what I want to do is go armed with a suitable CU and work out all the unknowns when I am there.
So given the big loads, particularly the C50 12KW boiler, a big shower, a big cooker and a few unknowns, what I am really asking is does anyone know a CU that will cope with such big loads without the neutral bar melting and being back to square 1? I guess this shows a lack of confidence in any of the rubbish that's churned out these days.
Part of me says fix the burned out neutral in the Proteus and leave that for the boiler and fit a smaller CU for the other stuff, just so reduce the loading on the new CU.
It started out as "fix the burned out neutral bar" in one CU, and move the other CU to a new location.
I could replace the burned out neutral bar ( I have a spare) but told them I can't move the old CU, it needs a new one (no areseedee etc)
The logical thing would therefore be one new larger CU to replace the two existing ones.
BUT
Here's the loads:
12KW electric boiler presently on a C50
Immersion B16
smokes B6
Cooker B50
Shoiwer B40
Sockets B32
Sockets B16
Water Heater B40 *
Unknown B40 *
Lights B15 *
Unknown B32 *
It's the little Proteus CU with the C50 that has the burned out neutral bar.
But on the main CU it's the last 4 that worry me. B40A water heater? WTGrape is that? Lights on a B15? and what's the unknown circuits on a B40 and a B32
Clearly this can't all be settled without a visit to determine the unknowns.
Anyway what I want to do is go armed with a suitable CU and work out all the unknowns when I am there.
So given the big loads, particularly the C50 12KW boiler, a big shower, a big cooker and a few unknowns, what I am really asking is does anyone know a CU that will cope with such big loads without the neutral bar melting and being back to square 1? I guess this shows a lack of confidence in any of the rubbish that's churned out these days.
Part of me says fix the burned out neutral in the Proteus and leave that for the boiler and fit a smaller CU for the other stuff, just so reduce the loading on the new CU.