Hi all,
Performed an EICR today in a 2 bed flat.
The consumer unit appears to have been relocated in the last few years from a small cupboard so that a combi boiler could be fitted.
Whoever moved the consumer unit did a job at it.
They have fitted an isolator where the consumer unit was and run 16mm tails to the new location, around 5 metres away.
No glands or grommets used on junction boxes or isolator.
The main issue I had was that when carrying out end to end tests on the ring final circuits (from the consumer unit) I noticed that the values were minimal.
I decided to open up a junction box where some of the circuits had been extended and found a mess - the rings had been connected in choc blocks and extended with 2x 2.5mm to the board. Is this against regs as it's figure of 8 or just bad practice?
I can see it'll definitely trip up the next inspector and so I'd like to at least put a C3 to improve and put a Wiska relocation box or similar.
What's your thoughts?
Images attached.
Performed an EICR today in a 2 bed flat.
The consumer unit appears to have been relocated in the last few years from a small cupboard so that a combi boiler could be fitted.
Whoever moved the consumer unit did a job at it.
They have fitted an isolator where the consumer unit was and run 16mm tails to the new location, around 5 metres away.
No glands or grommets used on junction boxes or isolator.
The main issue I had was that when carrying out end to end tests on the ring final circuits (from the consumer unit) I noticed that the values were minimal.
I decided to open up a junction box where some of the circuits had been extended and found a mess - the rings had been connected in choc blocks and extended with 2x 2.5mm to the board. Is this against regs as it's figure of 8 or just bad practice?
I can see it'll definitely trip up the next inspector and so I'd like to at least put a C3 to improve and put a Wiska relocation box or similar.
What's your thoughts?