Fitted a selv fan for a customer who has a tiny bathroom but it's not clearly any steam at all. It's well ducked outside and the fan runs fine.
Is there anything I can try to help him?
I understand natural air flow might help from even the bathroom door being slightly open but there must be a better way for circulation?
From my experience there are four typically issues;
(1) Fan not strong enough.
(2) Duct too long.
(3) Unable to allow equivalent amount of air into the room at the same rate that you are trying to extract.
(4) Fan not running for a long enough duration after the room has been used. (building regs recommend 15mins run-on for bathrooms without an opening window.)
When you say "well ducted", Do you mean its a longer run through a loft void rather than just a core-drill hole through the wall?
Most axial fans are only sufficient for a direct through the wall sort of duct length, e.g. less than 500mm long.
For longer duct runs you generally need a centrifugal fan that can push air further. (same principal as trying to blow through a drinking straw -vs- blowing through a hose pipe. need more force!)
Have a look at the spec of the fan for what rate of volume of air it can move..
Decent centrifugal fans can move double or triple the volume of cheaper axial fans.
Sufficient air flow is not optional, it is essential. otherwise the air will not move..
(Just as if one end of a drinking straw is partially blocked it will restrict or stop any flow).
Consider a 100mm vent-duct area is 7855 square mm, (or 78sqr cm)..
A 760mm door would need 10.3mm gap at the bottom to allow the same amount of air movement.
Also thick pile carpets on the outside of the door will also restrict air flow when the door is shut.