What would you code a solar PV sharing a RCD with other circuits ?
I just did a eicr and noticed this, so I mentioned it to the customer and explained that the .4 disconnection may not be meet because of the PV.He was not having any of it and saying it must be OK because it was done professionally and asked what reg it did not comply with.I couldn't think of one and said in my opinion it was poor practice. I also test the RCD and the PV shut down in 35ms.
I just did a eicr and noticed this, so I mentioned it to the customer and explained that the .4 disconnection may not be meet because of the PV.He was not having any of it and saying it must be OK because it was done professionally and asked what reg it did not comply with.I couldn't think of one and said in my opinion it was poor practice. I also test the RCD and the PV shut down in 35ms.