Just started a new build today the size of the property is 55000sq feet pretty big, so we will be putting in a sub board in splitting it roughley in half.

In total for the half the sub board is goin there will be around 100 downlights up and down being on 4 6a cb and 50 sockets up and down with that being on 2 32a cb.

My boss has told me we will run a 16mm t&e and a 10mm earth in as well, the length of the run is approx 20 metres back to the 1st ccu.

So is 16mm suitable?

Thanks very much

 
I would rather not run 16mm t&e would prefer 16mm swa no need for the extra 10mm earth then.

Total maximum demand for the breakers you are putting in with diversity would be 37amp

(add all used breakers together and multiply by 0.42) Round up if you get .***

16mm swa would also be about

 
whats the chance of it needing more power in the future? maybe 25mm SWA just in case?

and dont forget your volt drop includes submain and final circuit, so the less you have on submain, the more you can have to the final circuit

 
I'd go swa as GH says, you could go 2 core & use the armour as cpc (from memory the armour is equivilant to 50mm )

 
Armour csa

1.5mm = 17

2.5mm = 20

4.0mm = 22

6.0mm = 36

10mm = 42

16mm = 50

25mm = 70

35mm = 78

And if you use the big stuff

50mm=90

70mm=131

95mm=147

120mm=206

And if your strong enough

150mm=230

185mm=255

240mm=289

300mm=319

400mm=452

Two core with armour as cpc no need for discrimination of downside rcd and an equivelent og 50mm cpc cant go wrong! (unless you gland it wrong of course)

 
Armour csa1.5mm = 17

2.5mm = 20

4.0mm = 22

6.0mm = 36

10mm = 42

16mm = 50

25mm = 70

35mm = 78

And if you use the big stuff
Applaud Smiley:^O:^O:^O:^O

50mm=90

70mm=131

95mm=147

120mm=206

And if your strong enough
:D :^O:^O

150mm=230

185mm=255

240mm=289

300mm=319

400mm=452

Two core with armour as cpc no need for discrimination of downside rcd and an equivelent og 50mm cpc cant go wrong! (unless you gland it wrong of course)
Nice post ther GH! :x

 
Thanks specs, you would need some big bicepts for the big stuff, I bought a hydrolic crimper for 300mm earth lugs used it once, should have gone to hire it.

 
use 400mm just to be safe

better to be safe than sorry:D

bob

 
run a 25mm split concentric cable.

overall diameter is smaller than swa also can be made off easier just like t&e

I called pirelli many moons ago and the earth part is 16mm.

 
ARMOUR_RESISTANCE.jpg
 
I am a little confused with those figures in the tables. The uneeda publication I have although it is 16th edition states that a 16mm swa three core armour is equivelent to 4mm copper and cannnot be used for pme connections. If this is a new build surely it will be pme or am I barking up the wrong tree here.

Batty

 
I am a little confused with those figures in the tables. The uneeda publication I have although it is 16th edition states that a 16mm swa three core armour is equivelent to 4mm copper and cannnot be used for pme connections. If this is a new build surely it will be pme or am I barking up the wrong tree here.Batty
Batty posted a link to here a while back

 
The use of internal cores, of both thermoplastic and thermosetting SWA cables, as a CPC and/or the use of separate parallel CPCs are not required for SWA cables to comply with BS7671 provided.

1.The operating temperature of the cable does not exceed 70

 
The use of internal cores, of both thermoplastic and thermosetting SWA cables, as a CPC and/or the use of separate parallel CPCs are not required for SWA cables to comply with BS7671 provided.1.The operating temperature of the cable does not exceed 700C.