Test a socket ring main.
My advice to you is to get the RCD's and RCBO's tested.
The 2nd CU has been installed "poorly" by somebody who doesn't really understand the regs and to "hang" an EV charger off it wasn't a great move.
Without proper test kit and competence you are wasting your time
A single pole rcbo only disconnects live in the event of tripping, it leaves the neutral connected. Certain applications require a 2 pole protection device that disconnects both.
You can guess all you like... you'll be right eventually
... as others have said tripping can be one big issue or a result of many smaller issues. With appliances, wiroing This can cause much head scratching
After checking for visible water issues or cable damage you need a methodical approach and some test gear to narrow this down
Only a EV charging point by a qualified installer last August which is on a separate RCD.
Looking at the distribution arrangement I would have to ask an installer qualified in what, I doubt the proper application process has been carried out for the extra connected load of an EV and looking at the size of the sub main to the bar I doubt any calculations have been done to verify it has the capacity to feed an EV chargepoint as well as the bar which I would assume is heated using electric heaters so it is likely that it is overloaded at times
Qualified electrician required. Your son should be able to contact one.
100% and were on it thanks. Just very strange that this starts now after 4 years. I really think its something between each socket in the walls.
Electrical installation cables, accessories, joints etc.. deteriorate over time with usage..
(Hence why it is recommended to do periodic inspection and testing on older installations)..
So it is perfectly normal for a fault to occur after a period of time, rather than immediately following being first installed.
So translating to electrician speak, he has found a fault in a cable, it is too difficult to replace it, so he is proposing not to, and instead split it into two separate radial socket circuits?
Write your reply...