Denker, TT at the outbuilding fault goes to earth via the rod, the next rod this fault is likely to see is your PME rod at the house?(which is connected to, wait for it, the NEUTRAL)
or do reckon the fault will know this and decide to just go to the rod at star point instead?
this is why PME bonds have to be so big, we have had this all before about PME inheriting(pulling in) faults from external rods,
BTW, this TT fault could also manifest itself through any extraneous metalwork in the house too, down the MEBs to the MET where it will magically disappear into the ether, instead of going down the earthing conductor into the neutral.
or do reckon the fault will know this and decide to just go to the rod at star point instead?
this is why PME bonds have to be so big, we have had this all before about PME inheriting(pulling in) faults from external rods,
BTW, this TT fault could also manifest itself through any extraneous metalwork in the house too, down the MEBs to the MET where it will magically disappear into the ether, instead of going down the earthing conductor into the neutral.