Split tails to small cu for supply to a compressor/welder & one socket.
In the workshop new cu going in
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter10.jpg
cu in & wired. Tails come through wall in to trunking up to cu.
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter2.jpg
32amp outlet & rcd socket (socket supplied by customer)
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter3.jpg
Lead to welder connected.
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter1.jpg
While there I was asked to check some work they had done by another sparks. He is registered with Elecsa & according to the customer was a bit full of himself, while chatting he told them he'd done a month course to get approved & qualified as an electrician. But they used him as a favour (he's old man is a close freind) as he'd only just set himself up
Anyway I this is what he installed connected directly to supply via henleys.
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter5.jpg
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter4.jpg
The 63A 30mA supplies another cu in the garage/workshop for 2x ringmains & 2x lighting circuits.
He was asked to quote for a cu change & add 3 sockets, but told the customer he would have to rewire the workshop as he couldnt reuse the old T/E as he hadnt installed it:C
His price to rewire
In the workshop new cu going in
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter10.jpg
cu in & wired. Tails come through wall in to trunking up to cu.
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter2.jpg
32amp outlet & rcd socket (socket supplied by customer)
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter3.jpg
Lead to welder connected.
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter1.jpg
While there I was asked to check some work they had done by another sparks. He is registered with Elecsa & according to the customer was a bit full of himself, while chatting he told them he'd done a month course to get approved & qualified as an electrician. But they used him as a favour (he's old man is a close freind) as he'd only just set himself up
Anyway I this is what he installed connected directly to supply via henleys.
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter5.jpg
http://i83.photobucket.com/albums/j293/gazjothomas/P%20down%20school/carter4.jpg
The 63A 30mA supplies another cu in the garage/workshop for 2x ringmains & 2x lighting circuits.
He was asked to quote for a cu change & add 3 sockets, but told the customer he would have to rewire the workshop as he couldnt reuse the old T/E as he hadnt installed it:C
His price to rewire
- 2x ring finals totaling 16 sockets (why 2 rings they are in the same workshop/garage measuring 12mtrs x 9mtrs).
- 2x lighting circuits (8 inside on one circuit 4 outside on other).
- 1x new cu in garage/workshop.
- 1x 6mm T/E submain from meter to new cu.
- 1x (at the meter) enclosure with rcd as main switch & ocpd a 40amp mcb.