TT Board

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Jonnyboy 68

Junior Member
Joined
Apr 25, 2010
Messages
26
Reaction score
0
hi all

Just replaced an old CU installation with a 17th edition board and installed earth rod & pit etc ... enjoyed it .. my first TT and all's gone well !!! The board I installed was 12 way split 5+5+2. I intended to use the two unprotected ways for the smoke alarms and a dedicated fridge/freezer circuit in case of nuisance tripping. However being my first TT, I've re-read my regs and they state that ALL circuits on a TT have to be RCD protected ??? I've done my reading and therefore wanna use a 100mA RCD 'S Type' as my incoming main switch ... this is ok ?? However, I have QVS and TLC around here but only TLC seem to do a Wylex 100mA time delayed RCD and it's a bit steep at

 
can't all your circuits go on the 30ma splits?

opps just re-read

but does your cable/depths allow for non rcd?

 
You cannot Rcd main switch as this will not comply with 17th because if you have a fault on any off the two circuits you will lose all your power which is why you have two RCD's in board.

 
not saying what was right or wrong andy just the op suggestion

 
batty he was going to fit a higher rated rcd to give discrim
Yep ! Although....

No so much the higher rating as the discimination would only be provided by to the Time delayed aspectof the 100ma R.C.D.

 
If one circuit on the "non protected" portion of the board were to be on an MCB and the main switch was a 100mA RCD, then in the event of an earth fault on that circuit the RCD would trip. Since the RCD is the main switch, then the whole installation is now off.

RCBOs for the "non protected" ways would be the only way to comply I believe.

 
If one circuit on the "non protected" portion of the board were to be on an MCB and the main switch was a 100mA RCD, then in the event of an earth fault on that circuit the RCD would trip. Since the RCD is the main switch, then the whole installation is now off.RCBOs for the "non protected" ways would be the only way to comply I believe.
So now the question SP or DP??????

 