Evening all I'm just after some advice on the wiring of the above boiler..
The plumber has wired it as a 4 pipe system.
the system consists of the boiler which is a combination boiler
A cylinder with a 13 amp immersion heater (used as back of up if boiler breaks)
cylinder stat
Room stat
Programmer for heating and hot water
Pump out in the field wiring for instant hot water
Programmer for field pump to programme pump to run at certain times for instant hot water..
I've wired the system as an s plan
So Permanent Live and Neutral to Boiler
Live out from programmer to Common on Room stat
Live out from programmer to Common on Cylinder Stat
Switch live from Room Stat onto the boiler
Switch live from Cylinder Stat to Brown on the motorised valve
Switch live from the Orange on the valve to a cylinder demand junction box sited inside the boiler..
Heating works fine when the programmer for hot water is off (I. E.no permanent live to Cylinder stat)
When the hot water is set to auto or override the Cylinder stat receives a perman entry live and with cylinder stat set to 60 degrees the switch live from the cylinder stat returns to the coil on the valve (brown) and fires the boiler..
the problem I'm having is the hot watER demand is permanently showing as on at the boiler (small tap symbol)
the water from the tap is red hot so it has Deffo reaches 60 degrees but isn't switching off...)
Is my understanding correct here stat set to 60 water reaches 60 boiler should switch off??
I've turned the stat down to 45 and it clicks and voltage goes to 0 volts on the Orange wire (which I'd expect)
Is my set up and thought process correct here?
Sorry it's long winded but hopefully it's clear
Title should say s plan not Sunday plan (predictive text :Salute )
The plumber has wired it as a 4 pipe system.
the system consists of the boiler which is a combination boiler
A cylinder with a 13 amp immersion heater (used as back of up if boiler breaks)
cylinder stat
Room stat
Programmer for heating and hot water
Pump out in the field wiring for instant hot water
Programmer for field pump to programme pump to run at certain times for instant hot water..
I've wired the system as an s plan
So Permanent Live and Neutral to Boiler
Live out from programmer to Common on Room stat
Live out from programmer to Common on Cylinder Stat
Switch live from Room Stat onto the boiler
Switch live from Cylinder Stat to Brown on the motorised valve
Switch live from the Orange on the valve to a cylinder demand junction box sited inside the boiler..
Heating works fine when the programmer for hot water is off (I. E.no permanent live to Cylinder stat)
When the hot water is set to auto or override the Cylinder stat receives a perman entry live and with cylinder stat set to 60 degrees the switch live from the cylinder stat returns to the coil on the valve (brown) and fires the boiler..
the problem I'm having is the hot watER demand is permanently showing as on at the boiler (small tap symbol)
the water from the tap is red hot so it has Deffo reaches 60 degrees but isn't switching off...)
Is my understanding correct here stat set to 60 water reaches 60 boiler should switch off??
I've turned the stat down to 45 and it clicks and voltage goes to 0 volts on the Orange wire (which I'd expect)
Is my set up and thought process correct here?
Sorry it's long winded but hopefully it's clear
Title should say s plan not Sunday plan (predictive text :Salute )