Hi all
I have a job to supply a new 2 way board in outhouse. Am planning on running it from a 32 Amp MCB in 4mm twin and earth to adaptable box to outside and then 4mm SWA from there. The twin and earth is 7 metres and the SWA about 25 metres. My calcs for voltage drop comes in at 4.7% but this is at the full load of the 32 amp MCB. Obviousky 4.7% is higher than the 3% stipulated for lighting. Would others be concerned about this and increase cable to 6mm. Thanks
I have a job to supply a new 2 way board in outhouse. Am planning on running it from a 32 Amp MCB in 4mm twin and earth to adaptable box to outside and then 4mm SWA from there. The twin and earth is 7 metres and the SWA about 25 metres. My calcs for voltage drop comes in at 4.7% but this is at the full load of the 32 amp MCB. Obviousky 4.7% is higher than the 3% stipulated for lighting. Would others be concerned about this and increase cable to 6mm. Thanks