I doubt if I would be just using visual inspection to establish cable lengths...
:C
Surely it would be more appropriate to do a continuity measure such as R1+R2, or even R1+RN, (or both!) then use table 9A (pg 166 OSG) to calculate the circuit lengths...
Also I would NOT be relying on just measuring a voltage, (that can fluctuate anyway), to confirm any volt drops to base my costings on for any potential upgrade alterations work!
If you do a R1+R2 and an RN+R2 they should be within a gnats testicle of each other..
and R1+RN would be proportional to the 'R2' readings depending if different sized CPC used.
It could be that there is a concealed junction box somewhere with a high resistance joint causing some loss of voltage...
say a bad joint on Live or Neutral somewhere down the long run....
Don't forget that where the circuits exceed 100m the permissible voltdrop can be increased by 0.005% per meter up to a max 0.5%
(pg 358 Big Red).
And that the suppliers voltage can be anywhere between 216.2v - 253.0v
(pg 242 Big Red)
so just measuring it is of limited value?
Consider a scenario that you do a load of upgrade work then the customers moans that the lights a still dim!
and wants you to do more remedial work to rectify the problem at no extra cost.!
If I were doing this I would be have a fair few accurate calculations of the existing arrangement to base my recommendations on.
:coffee
:C
Surely it would be more appropriate to do a continuity measure such as R1+R2, or even R1+RN, (or both!) then use table 9A (pg 166 OSG) to calculate the circuit lengths...
Also I would NOT be relying on just measuring a voltage, (that can fluctuate anyway), to confirm any volt drops to base my costings on for any potential upgrade alterations work!
If you do a R1+R2 and an RN+R2 they should be within a gnats testicle of each other..
and R1+RN would be proportional to the 'R2' readings depending if different sized CPC used.
It could be that there is a concealed junction box somewhere with a high resistance joint causing some loss of voltage...
say a bad joint on Live or Neutral somewhere down the long run....
Don't forget that where the circuits exceed 100m the permissible voltdrop can be increased by 0.005% per meter up to a max 0.5%
(pg 358 Big Red).
And that the suppliers voltage can be anywhere between 216.2v - 253.0v
(pg 242 Big Red)
so just measuring it is of limited value?
Consider a scenario that you do a load of upgrade work then the customers moans that the lights a still dim!
and wants you to do more remedial work to rectify the problem at no extra cost.!
If I were doing this I would be have a fair few accurate calculations of the existing arrangement to base my recommendations on.