EICR has just been carried out for a rental property which i own -I'm keen to understand if the work is really required or if it's upsell?
Price of quote for remdial work is higher than previously intimated and with lower spec parts which concerns me.
It's been failed based on several points. I'm a layman when it comes to electrical works but I note from my own research that plastic fuseboard guideline is a C3 not a C2 though it seems to have been bundled into the latter here.
Several items listed on the report- all as C2 s:
DB : 4.3 Condition of enclosure(s) in terms of IP rating etc (416.2) - Top of the DB/CU has an unused opening exceeding IP4X with no access to live
parts (416.2.2) Side, bottom or front of the DB/CU has an unused opening exceeding IP2X (416.2.1) Clip in blanking plate fitted to DB/CU (complying
with BS EN 60/61439-3) is not secured with sufficient stability and durability, and is an IP rating issue (416.2.3;134.1.1;113.1;522)
2
DB : 4.4 Condition of enclosure(s) in terms of fire rating etc (421.1.201; 526.5) - CU in a domestic household premises is not metal or installed in a
non-combustible cabinet, showing no signs of thermal damage, located in the sole means of escape for a dwelling area (421.1.201) The DB/CU has
excessive hole in the rear of the enclosure fixed to flammable surface and has no signs of thermal damage (527.1.1)
3
DB : 4.14 Compatibility of protective devices, bases and other components; correct type and rating (No signs of unacceptable thermal damage, arcing
or overheating) (411.3.2; 411.4; 411.5; 411.6; section 432.433) - RCCB has not been selected appropriately for diversity, taking account of possible
circuit loadings, and is not equal to or greater than its main supply current rating – signs of overheating and thermal damage (522;536.4.202)
4
DB : 4.18 RCD(s) provided for fault protection - includes RCBOs (411.4.204; 411.5.2; 531.2) - Selectivity not achieved with series-connected RCD –
Safety concerns present (531.3.2;536.4.1.4)
5
DB : 5.17.4 Adequately connected at point of entry to enclosure (glands, bushes etc.) (522.8.5) - Un-bushed cable entry (stranded cables) –
mechanical strain/damage (522.8.1/5)
Also agreed limitations stated as
"No floor wall or ceiling spaces visibly inspected. Heating supply not live tested."
I'd like to know:
1. would you fail the EICR based on above?
2. What remedial action would you advise eg replace fuseboard/ block holes/openings with suitable plugs/ install into non combustable cabinet.? My priority is to keep costs low while meeting the standard for rental properties.
3. Should i be concerned about the agreed limitations? I understand the heating supply has been dead tested but not live tested as it's a economy 7 storage heater so no power during the day when the test was conducted.
2
3
4
5
I'd like to know: