Went on a callout yesterday, burning smell from shower switch. On inspection I discovered burnt neutral on load side. Checked the cable sizing which is 6mm and shower rating is 9.5kw. Am I right in saying there is no diversity on an electric shower? And if not why has the 32amp not been tripping since it was installed? (faulty breaker)? I told the customer that he needs a 10mm cable in or replace the shower to a lower wattage unit. I'm due back there to test the circuit later but I'm not sure if I'm missing anything.
Missing a few bits off me thinks....
9.5KW Will be the manufactures 240v rating
9500/240 = 39.5amps approx..
39.5A - 32A = 7.5A not a vast amount of extra currant running for a short duration not too much of a problem..
Using R1+R2 you can calc the cable length..
But TBH not many average domestic shower circuits are much more than 15m or 20m long tops!
Page 52 OSG..
clipped direct 6.0mm can take 47 amps
In conduit 6.00 can take 38 amps
If buried under loadsa insulation obviously drops down..
BUT as you already say it has been running on a 32A breaker..
not tripping..
which 32A is the rating for method A enclosed in conduit AND buried in an insulated wall!
so back to reality...
Your fault "Overheating at switch"
Is a LOSE connections when the switch was fitted..
Is it a cord pull?
If yes.. is it a square switch?
If Yes again put a circular Crabtree shower switch in.
e.g.
http://www.screwfix.com/prods/90597/Electrical-Supplies/Switches-Sockets/White-Moulded/Crabtree-Range/Crabtree-50A-Pullcord-Sw-Neon
Put a decent switch on ..
And tighten up ALL connections...
Double check connections at CU and Shower as well..
Double check insulation resistance to verify cable has NOT been damaged!
Stick a clamp meter on just to see what it is actually drawing.
all will be fine..
If you want to you could move any insulation from the cable in the loft
also you could stick a 40A breaker in IMHO..
Is it RCD protected?
UNLESS of course the customer is considering rewiring.. in which case stick in a new 10mm circuit...
and obviously if you are doing new installs or re-wire you'd be sticking in a 10mm
but if the installation is existing... and it will be lots of disruption to the decoration.. The 6.0mm will still work..
Balance of Best ideal regs solution -vs- Best safe feasible solution in customers budget.
:coffee
---------- AUTO MERGE Post added at 11:41 ---------- Previous post was at 11:39 ----------
AH...
PC's been replying while ole slow paws has been typing.