Guys,
I've done some cable calculations (from the book) and tried to confirm them using an online calculator and they've come out slightly different so I'd appreciate it if someone could double check me.
It's a 3 phase TNS supply with a Ze of 0.39ohms, I want to run a 3 phase SWA submain 32m from this protected by 100A HRC fuses. I've calculated the demand per phase to be 78A 79A & 86A (after diversity),,,, having domestic type final circuits including 2 x 50A submains a further 10m and 16m away supplying separate accommodation. Part of the submain (first one) will be underground, the other two will be T&E clipped direct.
I've calculated that the first submain should be 50mm (according to BRB) and the online calculator (Doncaster cables) came up with 25mm but with a volt drop of something like 6.5V:O
I've done some cable calculations (from the book) and tried to confirm them using an online calculator and they've come out slightly different so I'd appreciate it if someone could double check me.
It's a 3 phase TNS supply with a Ze of 0.39ohms, I want to run a 3 phase SWA submain 32m from this protected by 100A HRC fuses. I've calculated the demand per phase to be 78A 79A & 86A (after diversity),,,, having domestic type final circuits including 2 x 50A submains a further 10m and 16m away supplying separate accommodation. Part of the submain (first one) will be underground, the other two will be T&E clipped direct.
I've calculated that the first submain should be 50mm (according to BRB) and the online calculator (Doncaster cables) came up with 25mm but with a volt drop of something like 6.5V:O