I was asked to do some work at a medium sized house ( used to an old village school now converted), when I look at it prior to fitting a new DB. I found that the property could really!! do with rewiring. So in discus-ions with the client "ie so what do you want if we are changing it all?" he has asked for,
45 light fittings 13A
1 large all electric cooker (15KW),27A
a large expanse on electric underfloor heating (8KW)35A
immersion 9A
3 ring mains32A, 13A, 13A
future supply to garden office32A
after applying the diversity off the tables in guidance note 1 amounts in blue I come out with a load of about 174 A. My question is can all this be put on a single 100 a supply head. I have already brought the overall load down from over 300A when I persuaded him to not have electric showers.
thanks
Gavin