top banana
Member
Hi everyone,
A diversity question concerning 2 consumer units fed from 100amp DNO supply
Background, So I have an 18th Ed compliant consumer unit (DB1) fed by a 25m 2 core SWA into a IP rated box, the SWA is then split into 2*25mm tails feeding DB1 and a small 3 module enclosure incorporating an MCB and 100amp isolator, the MCB feeds a 10mm twin and earth submain to DB2., small 5 module garage type C/U
DB1 comprises SPD and RCBOs due to a TT earth system, there are 8 RCBOs highest rating 32 amps applying NAPIT diversity I have 100% of the highest rating 32amps, then 40% of all other circuits 16+16+20+20+16+6+6=100amps*40% = 40a+32a=72amps which doesn't exceed 100 amp main switch.
DB2 small garage consumer unit is fed by a 10mm twin and earth cable which is terminated into an MCB (32A) and 100amp isolator from the 25mm split tails, the garage consumer unit has 3 RCBOs (32,16,6 amps) 100% of 32amps, the 40% of other circuits = 16+6=22amps *40% =8.8A+32=40.8A
So as both DB1 and DB2 are fed by split 25m tails ultimately both are fed from a 100amp main DNO supply fuse and after diversity I have both DB1 and DB2, 72A+40.8A = 112A which is in excess of the main 100amp supply fuse is this correct? or do I apply diversity separately to each consumer unit as its split tails?
Many thanks in advance
A diversity question concerning 2 consumer units fed from 100amp DNO supply
Background, So I have an 18th Ed compliant consumer unit (DB1) fed by a 25m 2 core SWA into a IP rated box, the SWA is then split into 2*25mm tails feeding DB1 and a small 3 module enclosure incorporating an MCB and 100amp isolator, the MCB feeds a 10mm twin and earth submain to DB2., small 5 module garage type C/U
DB1 comprises SPD and RCBOs due to a TT earth system, there are 8 RCBOs highest rating 32 amps applying NAPIT diversity I have 100% of the highest rating 32amps, then 40% of all other circuits 16+16+20+20+16+6+6=100amps*40% = 40a+32a=72amps which doesn't exceed 100 amp main switch.
DB2 small garage consumer unit is fed by a 10mm twin and earth cable which is terminated into an MCB (32A) and 100amp isolator from the 25mm split tails, the garage consumer unit has 3 RCBOs (32,16,6 amps) 100% of 32amps, the 40% of other circuits = 16+6=22amps *40% =8.8A+32=40.8A
So as both DB1 and DB2 are fed by split 25m tails ultimately both are fed from a 100amp main DNO supply fuse and after diversity I have both DB1 and DB2, 72A+40.8A = 112A which is in excess of the main 100amp supply fuse is this correct? or do I apply diversity separately to each consumer unit as its split tails?
Many thanks in advance