Am I correct in thinking the fact that all 3 readings are >2000 means a wire has been cut through somewhere? No major work has been done to the flat between the two reports.
I would agree with your assumption..
A typical broken ring fault rarely has all three conductors totally open circuit..??
I have been on faults with similar symptoms to yours, which have been due to a socket front removed because it was going to be inaccessible behind some furniture..
But all they had done was wrap some PVC tape around each individual conductor, then put a blanking plate on the front of the old socket box!
And another one where two new sockets had been attempted to add to a ring...
But all they had done under the floor was cut the ring circuit cable..
Add two new junctions boxes on each half of the ring...
(which was good compared to the very common connector strip wrapped in tape joint found far to often!!)
Then connect the new socket cables onto the two new boxes..
BUT.. forget the join the two new sockets together as well to complete the ring..!!!!
{obviously no ring continuity dead testing before re-energising...
But it must have been correct as everything worked and the plug-in polarity tester gave all the right light indications!}
Basically, I have got to the stage now where very little stupid wiring surprises me especially where ring circuits are concerned and adding accessories spurred off rings!!!
I still can't see how a satisfactory EICR has been issued for a broken ring on a 32A protective device!??
Especially when they have written in black and white that a 32A 60898 type B MCB is connected to 2.5mm circuit with a 1.5mm CPC.. That simply CANNOT be satisfactory to any competent person!
The protective device MUST be a lower rating than the cable capacity to prevent damage to the circuit wiring..
More investigations are needed!