Mull this one over,
Customer rings me up asking for a second opinion on a pir that a local electrician had done on their rented property coutesy of the letting agent.
He conducted a visual inspection with the cert being a word document and came out with a few switches with no earths (been cut short) ok thats fine.
the main problems with the report were I found were that a code 1 was given to the cooker circuit being wired in ruber cable (I tested and came out with 20meg to earth), code 1 for No RCD protection, code 1 for undersized tails and main earth which are 25mm and 16mm?? Board is a 6way wylex rewireable fusebox.
At the bottom of the page in bold we have 'needs a full consumer unit with rcd protection' and also 'please note price for rectification cannot be provided due to property needing a full re-wire'
After a quick look tonight all switches have earths that need extending, cooker brings 20meg, quick global IR gives 1.8meg, fusebox has a blatant live part accessable which was missed off.
I can't beleive the words 'needing a full rewire'!
:red card
Customer rings me up asking for a second opinion on a pir that a local electrician had done on their rented property coutesy of the letting agent.
He conducted a visual inspection with the cert being a word document and came out with a few switches with no earths (been cut short) ok thats fine.
the main problems with the report were I found were that a code 1 was given to the cooker circuit being wired in ruber cable (I tested and came out with 20meg to earth), code 1 for No RCD protection, code 1 for undersized tails and main earth which are 25mm and 16mm?? Board is a 6way wylex rewireable fusebox.
At the bottom of the page in bold we have 'needs a full consumer unit with rcd protection' and also 'please note price for rectification cannot be provided due to property needing a full re-wire'
After a quick look tonight all switches have earths that need extending, cooker brings 20meg, quick global IR gives 1.8meg, fusebox has a blatant live part accessable which was missed off.
I can't beleive the words 'needing a full rewire'!
:red card