Which was indeed what I just said.additionally? the rule of thumb allows for the fact that when measuring the Zs the circuit is cold, and the resistance will be 'artificially' low, and pre-supposes that the circuit will be at normal operating temperatue when the fault happens
POST 4:- "@ normal operating temperatue! if not adjusted re Appendix 14."
POST 11:-"that allow for increased heat in a conductor during earth fault!
NICEIC quote these 80% values as the max value when testing cold conductors.."
It would appear with statements like that you are obviously not bud?of course it is pretty much irrelevant unfer the 17th edition anyway' date=' as most circuits need only be lower than 1667 ohms (can opened, worms everywhere)
but of course [u']i am not a real electrician so i am only guessing:^O
1667Ω is the limit to ensure 50v "touch voltage not exceeded"..... as in 1667Ω x 30ma = 50v
And I would assume you are not suggesting to ignore? .....
Big red book Pg 59:
411 - Automatic disconnection of supply415.1.2 The use of RCD's is not recognised as a sole means of protection and does not obviate the need to apply one of the protective measures specified in sections 411 to 414
412 - double or reinforced insulation
413 - electrical separation
414 - extra low voltage provided by SELV or PELV
"
Its probably not a lot of help to others just sticking out a bland statement like this without justifying it a bit for the benefit of others reading who genuinely would like to learn!Lets face it anyone can type any old statement just to cause confusion.. but it's not really helpful is it? ?:|of course it is pretty much irrelevant unfer the 17th edition anyway..."
I do hope you can put more positive input than this to the forum? and this has nothing to do with the reasons you have left your other place? :|
(Can closed Worms Squashed)! ; \
If I have miss interpreted your meaning here I appologise.. Lets hope for more constructive debate
oh there is also many an industrial / commercial application where RCDs not needed?
or even in a domestic.. with surface conduit to FCU suppling some fixed equipment? RCD? Nope!